Backdrafting Supply?

steamqueen
steamqueen Member Posts: 1

The supply pipe on this boiler looks sooty. Is it possible that the exhaust is backing up all the way through the boiler? Atmospheric ventilation. The excess air is high (34%). Thanks!

IMG_3715.JPG

Comments

  • Big Ed_4
    Big Ed_4 Member Posts: 3,180
    edited April 14

    I would check the chimney , pull the vent pipe away from the wall and check the chimney base. The base of the chimney could be plugged .

    I would also look for exhaust fans . An exhaust fan ,without make up air would drop the pressure in a closed building . Pull down from the chimney …

    Also have the boiler flue passage and the combustion checked ..