hot_rod
hot_rod Posts: 28,699

Strip away all the case, electronics, wiring and you get to the intersection of fire and water. Gas and air blend in the burner mounting passage, which is also the mounting plate for the fan and gas valve, very simple engineering. A spark starts the fire.

Properly installed and cared for this is a very durable, reliable and efficient HX design. I think easier to service compared to fire tubes, much less welding exposed to direct flame also.

Screenshot 2025-04-04 at 9.06.02 AM.png

This was a Knight I installed in my home many years ago. About a year into it it started throwing random low flow lock outs. I could never duplicate the issue when sitting in front of it. Checked all the typical flow obstruction issues, nothing.

Finally ripped it out, destined to be a parts boiler as I had many of this model installed for customers. I started sawing into the HX tubes on a quest for the blockage. Oddly I left that ell and nipple on the HX to clamp it into the vice, so I missed the hidden check before I started cutting.

The boiler circ was one of the early Grundfos ICFs. The first ones had a small diameter check which was not held in very well with the o-ring and plastic tabs on the side.

When I disassembled it the check had puked out of the circ and stuck in a 1" ell right at the boiler connection. It would turn to different positions in the ell, so flow would sometimes be fine.

Screenshot 2025-04-05 at 5.34.48 PM.png

I had filled it with good water and added Rhomar conditioner from day one.

The black you see on the tube I cut open is the film provider in the Rhomar. It looked lik a magic marker coating inside the tubes, very thin layer of color. This protects the stainless from aggressive fluids, low ph, or high chlorides in fill water without much if any heat transfer penalty.

I've been sold on boiler conditioners ever since.

Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream
Mad Dog_2109A_5PC7060ILikeEmOlderAlan (California Radiant) ForbesJUGHNE

Comments

  • Mad Dog_2
    Mad Dog_2 Posts: 8,755

    I've never been crazy about the plastic flow checks...did any manufacturer try a brass type? Mad Dog

  • hot_rod
    hot_rod Posts: 28,699

    I have not seen any of the circulator IFCs made out of brass or any metal.

    The solar pump stations have brass on brass seat checks, but they are in the isolation valve against the pump. A better location actually out of the more turbulent conditions the volute.

    I think Apollo/ Conbraco still make brass hydronic checks, maybe a rubber seat with a brass disc.

    Are most of the small circs built with plastic impellers? Possibly the same material as the checks?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • 109A_5
    109A_5 Posts: 4,759

    Interesting !!! At least you figured it out. In hindsight how would you troubleshoot an issue like that. Maybe ?

    image.png

    I suppose you know one more thing to look for now.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    hot_rod
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,328

    Better off not using the checks installed in the circs.

    What works in the lab doesn't always transfer to the field.

    PeteAdelcrossv
  • GGross
    GGross Posts: 2,104

    Had an internal flow check come out of a pump on a viessmann 399 one time. The HX design splits the supply and return into 2 separate S/R at the HX, high quality flow sensors on the outlet that watch for a minimum flow rate, as well as the differential between the two, if it gets too high it shuts down assuming there is a blockage in the HX. after many stressful days I finally gave the go ahead to pull the boiler and wouldn't you know it a little check valve was right there

  • hot_rod
    hot_rod Posts: 28,699

    I suspect we are not alone with this discovery.

    All in all the ICFs probably fix, or help more installations than they harm.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    GGross
  • GGross
    GGross Posts: 2,104

    Getting an installer to believe that the flow sensors are not defective and are just doing exactly what they are meant to can be quite the challenge I learned.

    mattmia2
  • Oftentimes, IFC's are not shown on the parts diagram. This was the case with a Viessmann 222 where I spent days looking for the blockage and only found it by accident. It was also a surprise revelation to the Viessmann tech. support guys.

    When flow stops in a system, there are the usual culprits: air in the system, bad pump and the occasional obstruction. The first two are easier to figure out than the last one and the last one can be many things.

    We need a more reliable IFC. Plastic components with a fragile spring just doesn't cut it.

    It should also be made easier to inspect. Have you ever tried to remove an IFC from a Grundfos volute?

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    mattmia2GGross
  • Grallert
    Grallert Posts: 1,237

     "Have you ever tried to remove an IFC from a Grundfos volute?"

    Always or nearly so they come out in pieces. PITB

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

    mattmia2JUGHNE
  • hot_rod
    hot_rod Posts: 28,699

    The tabs on the sides of those Neoperl checks do a great job of holding them in. As long as there is a groove or something for them to engage to.

    With a fine tolerance check, such as the ICF, a strainer is almost a must.

    Checks in 3 way and 4 way thermostatic valves always include screens. BUT, they need to be maintained, just like a Y strainer.

    The checks and screens in the under sink H style thermostatic are tiny.

    Screenshot 2025-04-07 at 10.17.42 AM.png

    When checks are new and lubed they slide in and out easily. Probably a week after use, not so easily :)

    Screenshot 2025-04-07 at 10.18.05 AM.png

    Springs have an expected service life like anything else. The systems with any air in them really cause the springs to get over-worked. The checks and springs chatter like geese eating dominos.

    Even un-reamed copper tube will create bubbles problematic for small low psi checks

    Screenshot 2025-04-07 at 10.32.20 AM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2
  • mattmia2
    mattmia2 Posts: 18,399

    I'm considering installing one of those to solve my now i have the indirect set hotter and need to mix in some cold to wash my hands but it is a 2 handle faucet and that is significantly more incontinent all day long than just turning on one handle problem. Also I don't think the american standard 2 handle cartridges are as heat resistant as they used to be after they switched from the beige to the black plastic.

  • mattmia2
    mattmia2 Posts: 18,399

    Then there is always the disgruntled contractor that dumps a bucket of ping pong balls in the piping.

    GGross
  • hot_rod
    hot_rod Posts: 28,699

    i know with the neoperl checks, the HT series, high temperature, are all black?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Posts: 18,399

    I mean the cartridges for the faucet. The ones that came with it 25 years ago and the first replacements would last for like a decade until the seals around the ceramic disc would leak, the ones I have got in the past 5 years or so last a year or 2 when the plastic that connects the disc to the stem cracks.

  • hot_rod
    hot_rod Posts: 28,699

    Composites, plastics, etc, whatever the use, plbg or hgt, when they are black it usually indicates carbon black has been added to the blend. This makes the material more thermally stable.

    So the engineers tell me.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Posts: 18,399

    what are  plbg and hgt? google was useless

  • hot_rod
    hot_rod Posts: 28,699

    plumbing and heating

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2
  • mattmia2
    mattmia2 Posts: 18,399

    oh, i read that wrong, i thought those were types of plastic…