  • Doegirl
    Doegirl Posts: 18

    Yes

  • Doegirl
    Doegirl Posts: 18

    Aside from the water heater and boiler I have a gas dryer,I tuned it on it felt hot but hmm my stove has been out first the oven burner wouldn't work & then my stove burners started have issues with the gas You asked both asked what kind of gas Is that a problem with the meter outside?

  • 109A_5
    109A_5 Posts: 4,761

    If all the gas appliances are having issues, you should call the Gas company. Once in a while the gas distribution pipes fill with water and the gas flow is severely degraded. You may have multiple issues too.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    rick in Alaska
  • mattmia2
    mattmia2 Posts: 18,399

    Your service regulator could be bad. That is the responsibility of the gas utility if it is natural gas.

  • Doegirl
    Doegirl Posts: 18

    I went outside to check the vent on the regulator I also knocked some debris off it with my finger before I took the pics

    1000001911.jpg 1000001912.jpg
  • mattmia2
    mattmia2 Posts: 18,399

    The vent can ice up when it is around freezing but that is far more common with propane. With natural gas it is more common that the regulator or meter will have some sort of internal failure.

  • Doegirl
    Doegirl Posts: 18

    Thank you, I'll call the gas company see what they say & change the thermocouple & go from there

    mattmia2
  • mattmia2
    mattmia2 Posts: 18,399

    The thermocouple may be ok, it might just not be heating the right part if the flame is too small because the pressure is low.

  • Doegirl
    Doegirl Posts: 18

    I thought it looked weak, I figured it was clogged but it didn't make a difference after taking it apart blowing air through the lines and cleaning it all with steel wool It had rust & debris in it and build up on the thermocouple