Radiant heat -snow melting

creger.robert
creger.robert Member Posts: 63

pro-cons

piping to manifolds etc. plastic pex fittings Verus brass(nothing underground)

what are your thoughts? system will have glycol

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,319

    @creger.robert Said: "(nothing underground)"

    How does snowmelt work if there is nothing underground?

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Mad Dog_2GGross
  • GGross
    GGross Member Posts: 1,456

    If the manifold is remotely mounted, which they nearly always are, I would use pex pipe to the manifolds and it obviously needs to be buried at that point. the buried supply and return piping should have no fittings except from copper inside the boiler room, and to a brass or stainless manifold, and should be insulated and sleeved. Fittings from copper to pex will need to be brass, from pex to manifold should be brass, I would recommend the piping in the boiler room be copper, and to use an irrigation valve access box for the remote manifold so you can access it if needed.

  • creger.robert
    creger.robert Member Posts: 63

    lol yes tubing is underground-im talking about a pex to pex connection brass or plastic

  • GGross
    GGross Member Posts: 1,456

    If the pex is buried then NO connections at all, if it is inside then transition to copper with a brass fitting, if you are piping the whole boiler in pex then just use whatever, highly recommend piping your boiler in copper though. Rarely if ever would I need to make a pex to pex connection on a typical snow melt install.

  • creger.robert
    creger.robert Member Posts: 63

    boiler is all copper-Im talking about extending pex mains to get it to boiler area-it is strictly a pex to pex connection

  • hot_rod
    hot_rod Member Posts: 24,773

    I prefer the brass pex connections

    If it is a splice underground they have a wrap tape to protect it.

    I don't think an expansion plastic fitting, Rehau, Uponor, Mr Pex, etc, would not need to be wrapped?

    Just remember flow rates will be lower in pex tube compared to equal sized copper.

    PPI website has a nice calculator for pex flowrates.

    https://plasticpipecalculator.com/

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,887

    Hows about some pictures of the boiler/s & mechanical room? Mad Dog