Airlock in oil

Had a weird thing happen today. No issues at all with steam boiler and Beckett AFG oil burner all winter. Had it cleaned and tuned up last May. This evening I noticed house felt cold. Tank is at least 3/8 full. Oil burner was locked out. I pushed reset once and no lights etc. sounded like it was trying to prime. I opened the bleeder under the pump and pushed reset. Oil came out and then a slug of air. Boiler running fine now. I’m just wondering why this would happen now vs earlier in the season. Our oil level in tank has gotten down to lower than this and no issues at all until now. Thank you for your advice.
Comments
-
Where is the oil tank?
How old is the tank?
Where is the oil filter, at the tank, or at the burner?
1 pipe or 2 to the burner?
If 1 pipe, does it come off the top or bottom of the tank?
If you opened the bleeder before starting the burner, and it's not gravity fed, you could have sucked air into the pump. Then the issue might not even be oil related.
If it happens again, call for service.
0 -
Its possible the gauge in the tank is bad and you are lower on oil than you think
0 -
oil tank is in basement and is about 10 years old.
Filter is at tank. One pipe. Comes off bottom and then goes up along ceiling.
Gauge is definitely accurate as there is a float gauge as well as ultrasonic.
I believe I opened bleeder after I pushed reset.
I’ll call for service if it recurs. Thanks0 -
That will happen with over head lines . Leaks , bad air primes and oil deliveries could add the air … I would recommend an Tigerloop ..
There was an error rendering this rich post.
0 -
-
it’s been three days and no recurrence. I guess I’m just wondering why it hasn’t happened again. Could it have just been a one off?
0 -
Not likely. In my experience things mechanical never "heal" themselves. Overhead line can be problimatic.
If it was mine I would take apart every fitting and check all flares and pipe joints. Also the oil filters can leak in a little air. The air got in there somehow.
Most people will tell you to put a Tiger loop on it. I consider it a band aid and would use a two pipe system instead. But that is JMHO
0 -
Running a 1 pipe oil line up, over, and down can cause air issues over time. Especially if the filter at the tank needs replacement. A vacuum gauge at the burner would tell you. Avoid hills and valleys on the horizontal run. Keep it as straight and seamless as possible.
0
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 105 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 104 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 952 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements