Triangle Tube Challenger DHW not going above 100F

HeatingHelp
HeatingHelp Administrator Posts: 700
This discussion was created from comments split from: Triangle Tube Challenger domestic hot water does not maintain temp.

Comments

  • Mikey318
    Mikey318 Member Posts: 1

    Looking to understand more about these systems. Just bought a place and the DHW is not going above 100 deg. Looking for good starting points. Thanks

  • HeatingHelp.com
    HeatingHelp.com Member, Moderator, Administrator Posts: 135

    Welcome @Mikey318 - I created a new thread so your question about your particular system wouldn't be lost at the bottom of an old thread. It would also be helpful to post pictures of your system to help our community troubleshoot your issue.

    Forum Moderator

  • GGross
    GGross Member Posts: 1,466

    First thing to do would be to confirm the setpoint outlet temp of the unit, and record the temperature at the fixture. Take note of any mixing device on the unit, and anti-scald valves at any fixtures. pictures help

  • Intplm.
    Intplm. Member Posts: 2,572

    From where are you getting the temp. measurement of 100 deg.? Is it from a shower, lavatory or kitchen sink?

    GGross