Missing Main Vent

mdmhh256
Member Posts: 30
1 pipe, gas steam system. 2 main loops with dry returns. one loop has a vent on the return just before it drops to the boiler (although I am not sure it is working). The other loop has no vent
, but there is a capped T just below where the return drops to the boiler (see photo). Two questions…. (1) Is it ok to put a vent into that T ? (I presume replace cap with an elbow and run a several inch nipple up with the vent at the top?) (2) does it matter on the venting capacity of a main vent, or just go for the fastest one available. Thanks
-1
Comments
-
- Yes, not ideal, but convenience counts. Come out full size and then use a reducing ell to your nipple going up. Go as high as possible.
- Vents should some relationship to main size. And since you have two, you'd want them to fill with steam at approximately the same time.
Can you provide the size and approximate length of each main?
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements