How to properly purge my system?

cbassett5477
cbassett5477 Member Posts: 2

Newbie and New homeowner…I had a leak that I fixed. I have looked on how to purge my system but haven't had much luck. Maybe if someone could tell me how my system is supposed to work, I would have better luck. I am not sure what valves are supposed to be open and closed while purging. I have enclosed pictures of the system, some are labeled. I would really appreciate the help. Thanks! (Yes, I still have the pressure pipe off.)

Comments

  • hot_rod
    hot_rod Member Posts: 24,322

    there should be large screwdriver slots in a brass piece just above the pumps. Those are isolation flanges, a ball valve without a handle. Turn the slot 1/4 turn CW, attach hose above on the hose valve

    Maybe spray penetrating oil on those screws for a day, they tend to sieze up

    They should be in either side if both pumps , so you have two options😗

    The beige valve in the 3rd pic is the autofill, lift the lever to get fast fill, but watch the pressure, stay below 30 psi

    Often when you mess with old fill valves they tend to nit work after use, so you may need to shut it off replace it possibly It should be set to 12 psi, if pressure exceeds that, it is done. What is the prey currently?

    It should have a back flow device paired with it, to be safe and legal, and a shutoff

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • cbassett5477
    cbassett5477 Member Posts: 2

    Thanks! I will check it out. I am getting 12psi!