Nest Thermostat power issue
![RyanNYC1](https://secure.gravatar.com/avatar/4aa10d56a8596ae60a80ee179ad9bfb9/?default=https%3A%2F%2Fvanillicon.com%2F897ad67d6d9f63e422a7aeaf6beb7655_200.png&rating=g&size=200)
I have the following setup:
-Weil McLain EG-65 steam boiler
-McDonald & Miller Unimatch Water Feeder
-Safgard 400 Series Low Water Cut-Off
-Nest Thermostat (wiring: white wire into the W1 slot, red wire into the RH slot).
Problem:
When the low-water indicator flashes on the Safgard Low Water Cut-Off, the Nest thermostat shows “no power.” After the automatic feeder adds water, the Nest turns back on after a few minutes.
Is there a way to prevent this issue?
Comments
-
To be reliable the Nest needs constant 24 volt power. Power comes in on the R wire but you need a "C" or common wire for them to work
The issue is that the Nest has a large battery that needs charging. They are supposed to recharge on the off cycle. Some boilers do not have a large enough transformer to charge the nest even with the C wire.
The best way in my opinion is to add a separate
transformer and relay. Others may comment with other ideas. This is just my opinion.
See the attached
2 -
You can power the thermostat using R and C on the transformer to Rc and C on the thermostat. Then Rh and W on the thermostat to G and Y on the transformer thermostat wires.
0 -
What @HVACNUT suggestion may or may not work. Read this comment for how to use an isolation relay
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Here is the diagram from the comment:
And to add the relay would look like this based on your equipment's diagram
The relay on the top Combination Relay/Transformer that I added may look like the transformer that is powering the burner, but it is not, The top is the additional isolation relay that is needed to properly set up your Nest Thermostat on this steam boiler.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Been there, you need to power the nest with full-time 24 V, which would likely require the use of a relay.
Or, run a 4 wire, two of the wires are the power and common, two of the wires are your call for heat.( r and w) . No relay needed in this circumstance.1
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 100 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 101 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 932 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements