Estimating new build yearly heating cost
trying to figure out an estimate on yearly heating costs for this new build. Plan is to install 1 ductless Minisplit 9,000 BTU. Then a ducted Minisplit 9,000 BTU as well. Total heating degree days in our area are 6,165. Also cost per KWH here is $0.125
  • GroundUp
    GroundUp Posts: 2,573
    Try the calc again on builditsolar.com and you can enter the design temp as well as the cost per unit of fuel, and it'll spit out a calculated estimate.
  • Kaos
    Kaos Posts: 1,007
    Your infiltartion loss seem on the high side, but not far off.
    Here is the math.
    6000HDD, I'm guessing design temp of 5F (so 60F delta T). your head load of 18k.
    18k/60f= 300BTU/degF
    300*6000HDD*24=432therms
    432therms*29.3=12657kWh of heat
    A heat pump would get you an average COP of around 3, so you need
    12657/3=4219kWh or $527.
    Cooling cost would probably be 1/3 to 1/4 of that.
    Hot_water_fan
  • @Kaos you nailed it. You can skip the therms piece and just use 3412 Btu per kWh.
