Arco AC 101B Steam

keith123
keith123 Member Posts: 105

would anyone having any sizing charts for these? Apparently there were two models. A 101B and a 201B.

I’m looking for the connected EDR ratings

Comments

  • mattmia2
    mattmia2 Member Posts: 11,235

    There's a steam coil in there? Is there also a blower in there? The output is going to be dependent on the coil and the airflow.(and the return temp). there is probably a chart in the old arco catalogs. i think there are some arco catalogs in the library here.

    keith123
  • keith123
    keith123 Member Posts: 105

    I did a search on this site already.

    The most I was able to find was in a 1938 catalog found on an archive website.

    Thank you though

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,934

    Start it up and take the air temp in and out. Then measure the cfm air flow. Get the BTUs you calculate and divide it by 240 for EDR or divide it by 1000 to give you LBs of steam.

    Easy calculation when you collect the measurements.

    keith123mattmia2