Ignition module without sensor tab on unit with two wire intermittent pilot.

EdwardP
EdwardP Member Posts: 1

I am attempting to get a Modine PAE500 furnace functioning which has a UT intermittent pilot module, It has a UT 1003-600A intermittent pilot control module. My question is that the pilot has 2 wires, the sensor wire and the ignitor wire, but the electronic module has the SPARK tab but there is no connector tab for the sensor wire.

Where does the sensor wire attach?

A response would be greatly appreciated.

Comments

  • Steamhead
    Steamhead Member Posts: 17,494

    How is the current one wired?

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • 109A_5
    109A_5 Member Posts: 1,921

    May not be the original ignition module, seems Modine did it both ways depending on the model. Some modules sense the flame through the Ignitor circuit.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System