Ignition module without sensor tab on unit with two wire intermittent pilot.
EdwardP
Member Posts: 1
in Gas Heating
I am attempting to get a Modine PAE500 furnace functioning which has a UT intermittent pilot module, It has a UT 1003-600A intermittent pilot control module. My question is that the pilot has 2 wires, the sensor wire and the ignitor wire, but the electronic module has the SPARK tab but there is no connector tab for the sensor wire.
Where does the sensor wire attach?
A response would be greatly appreciated.
0
Comments
-
How is the current one wired?
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
May not be the original ignition module, seems Modine did it both ways depending on the model. Some modules sense the flame through the Ignitor circuit.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0