Can high pressure on the boiler, I'm talking over 3 psi cause the air vents to continuously hiss and sometimes let out some water?

Comments

  • delcrossv
    delcrossv Member Posts: 1,916
    edited December 2024

    Yes. Especially if the vent is failing/has failed.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • Wcurtis
    Wcurtis Member Posts: 129
    edited December 2024

    Why is the boiler pressure so high, is the pressuretrol set up properly, working as intended, pigtail plugged, adequate low pressure gauge installed at the boiler….something to consider.

    This was my problem when I moved into the house and found pressuretrol set to 4 pounds, then had to replace several air vents although they had water in them (could have drained and blew through them and maybe would have worked but I wanted adjustible vents for balancing so they were replaced instead)

  • dopey27177
    dopey27177 Member Posts: 916

    Steam pressure should not exceed 2 psig..

    Set differential to 1/2 psig.

    You may need to replace pressure controller with a vaporstat.

    vaporstat settings 1 1/2 psig with 1/2 pig diffferential,