moving the wiring box from the taco 007 pump??

skimmer
skimmer Member Posts: 173

I have a friend who has a taco 007 in an extremely tight spot, no space on either side, crushing the electric hook up box on the taco. Feeding a hot water loop off a steam boiler and was forced to install it upside down, flow now going into boiler instead of away.

Getting terrible water hammer.

In order to flip it over in the right position, the electric hook up box has to be removed.

Is there a kit that allows you to mount the electric connections somewhere else? Ive seen an electric plug in kit..

its that bad, no space.. any ideas?

Comments

  • 109A_5
    109A_5 Member Posts: 2,095

    Hello skimmer,

    Maybe remove the 4 screws and re-clock the whole motor assembly.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    bjohnhy
  • skimmer
    skimmer Member Posts: 173

    Just spin the whole assembly?

  • 109A_5
    109A_5 Member Posts: 2,095

    Yes, spin the whole motor assembly 180 degrees so the pump pumps in the correct direction for the system and the electrical box is out of the way. However I have not tried it with a 007, maybe there is an indexing that prevents it. It works with other equipment if done correctly.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    PC7060
  • bjohnhy
    bjohnhy Member Posts: 96

    You don't need this whole video.

    The 4 hex bolts in corners.

  • hot_rod
    hot_rod Member Posts: 24,332
    edited December 2024

    with the water drained down out of the pump

    But flip the entire pump first if it is flowing the wrong direction ?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • 109A_5
    109A_5 Member Posts: 2,095

    Just happened to see this in an unrelated thread.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Joe Mattiello
    Joe Mattiello Member Posts: 732

    Release the pressure of the system, and rotate to motor assembly.

    Joe Mattiello
    N. E. Regional Manger, Commercial Products
    Taco Comfort Solutions
  • skimmer
    skimmer Member Posts: 173

    No what I mean is that the electric box stays on the right hand side as the photo shows above which is upside down.. can you leave it like that and remove the 4 bolts and turn it upside down so you reverse the flow but the pump install remains in the same position?

  • 109A_5
    109A_5 Member Posts: 2,095
    edited January 5

    Confused, what's the difference ? The thing that matters is the water is flowing in the correct direction for the system, which is the pump casting orientation to the system. The placement of the electrical box does not determine the water flow direction.

    If you remove the 4 screws that secure the motor housing to the pump casting and rotate one (the motor or the casting, pick just one) 180 degrees. The electrical box does not care what direction the circulator is moving the water.

    The pump casting has to be in the correct position to flow the water in the correct direction for the system.

    In the picture above of the two circulators, I bet the water is flowing in the same direction but the electrical box is orientated on the opposite side of one motor housings. Probably because they rotated it 180 degrees.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System