Viessmann B1KE f380 faults
![mattyc](https://secure.gravatar.com/avatar/28383e832183f75eb2ac20eb273cbf56/?default=https%3A%2F%2Fvanillicon.com%2F2471e837d36a3b0cade0a0bffcdc1b88_200.png&rating=g&size=200)
Out of several installations of the new Viessmann models of boilers (B1ke/B1he), most have worked flawlessly. On occasion, several units (so far only the combi boiler's) express an F.380 fault code which is flame loss immediately after stabilization. Resetting the boiler will have it running fine sometimes for weeks or months without further issue. The units that have the issue are all located in the same development and run on natural gas. Gas pressure is within ranges, combustion results are all within range. The fresh air and exhaust piping are sidewall vented. Clearance from fresh air to exhaust is correct according to the install instructions. I have tried replacing the ignition electrodes and the ionization electrodes and cleaned the heat exchangers. Sometimes this works, sometimes it doesn't. Sometimes we continue to have issues (Randomly). The only other thing with this specific development is that it is located about a mile or so off of the long island sound. The wind does blow through that area quit strong at times. Could high winds effect flame stabilization? Have any other installers run across this issue and had true fix for the problem? Thanks in advance.
Comments
-
What are the actual gas pressures?
the way to test is to record static pressure, the value after ignition, run to high fire and record the lowest value, turn off boiler and record the lockup pressure, ideally this is done with all gas fired appliances running. if you have a drop near or greater than 1.0" (0.5 ideally) wc you need to fix the gas line
What are the actual combustion results?
What size and how many elbows are on the exhaust system? (b1ke really needs minimum 3" poly) add together length and number of ells for both intake and exhaust
Where are the intake and exhaust located outside in regard to each other? The minimum clearances that ANY manufacturer give are only minimums, and can not guarantee that recirculation won't occur
My B1HE is located with the exhaust and intake facing directly at the wind, 50mph winds have never caused an error for me or any of my customers (several hundred out in the field) that is not to say it's impossible, and I certainly wouldn't recommend installing it like that, but I would record all necessary values and report back with pictures of the intake and the exhaust. On a relatively new install if I had to take a guess I would go at gas pressure and recirc, it's nearly always gas pressure or recirc
0 -
I have this exact same issue and can’t find a solution. Were you able to solve this problem?
0 -
Need more info, combustion issues can be several things what works for one might not work for the other, see my earlier comment in the thread, sometimes it's just a bad flame sensor, most of the time it has something to do with gas supply/venting/site issues that either cause combustion errors or foul up the flame sensor which causes issues. take measurements of your gas pressures, static and dynamic, record all values from static, to drop at ignition, run to high fire, and then shut it down. If you can get the boiler to run test the combustion and record all values. Check the flame sensor and igniter for damage or excessive wear.
0 -
-
I second the venting issue. Another option is to install a tee as a bullhead. That will slow the wind from blowing out the flame.
0 -
same problem.
I have many B1ke and B1he boilers out in the area I service including at my own house. I have one B1ke that started doing this same scenario within the first heating season. Spoke with viessmann, they sent me a new flame rod and it worked from a bit, cleaning it will sometimes get them through weeks sometimes a couple months. Always get a message (last time was yesterday that flame goes out after stabilization)
would love a solution. Will be back on with supplier and tech support shortly0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 100 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 101 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 934 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements