Tankless coil not getting priority
I have:
  • Weil-McLain WTGO-5 with tankless coil, no indirect tank
  • HydroStat 3250-Plus
  • Argo ARM relay board
  • 3 heating zones (one is the basement and rarely used)
  • There was previously an indirect tank but it started leaking and was removed; the circulator and priority zone wiring are disconnected
Short version of the problem: when the heat is on, the shower is cold.
The HydroStat recently went kaput and was replaced with the same model. The installer wired up T-T to X-X, set the Zone/Indirect switch to Z, set the limits to 160/190, and that's it. Now on cold days when one or more of the thermostats is calling and the circulators are running, the domestic coil isn't getting enough heat.
The HydroStat manual has wiring diagrams for giving priority to an indirect, but I can't find a diagram that matches this situation (tankless priority without indirect). I tried removing the ZC/ZR jumper on the ARM and connecting ZC/ZR from the HydroStat to the ARM, and switching the HydroStat Zone/Indirect switch to I. Everything works but it's still the same situation, cold showers when the house is calling for heat.
How can I get it to prioritize the coil and not run the circulators when the coil is below temp?
  • LRCCBJ
    LRCCBJ Member Posts: 1,043
    edited December 2024
    After pondering it a bit, the problem is that there is no way the Hydrostat can know that there is a HW demand from the coil. You'd need another aquastat mounted to the incoming cold water line. Run the the ground wire(s) from the circulator(s) through this aquastat. When it opens (due to 50F fluid), the circulators stop. It would recover fairly quickly at the end of the shower above a setpoint of 120F and restart the circulators. I'd probably set it at 120F because the boiler will never be below this value if it is operating.
    Unfortunately, this solution is not going to prevent a lukewarm shower if the boiler temperature is at 140F at the moment the aquastat opens.
    The tribulations of a tankless coil…………………………..
  • riny
    riny Member Posts: 18
    Sigh, thank you. I think you're right that there's no way to measure demand on the coil. But I did make one more change this afternoon… I disconnected T-T, leaving only ZC-ZR connected, and set the switch back to Z. Now whenever the stat temp drops below the low limit, it cuts off the circulators. That should let all of the heat go to the coil until the boiler temp is back up above 160. I haven't tried it yet but I'm afraid the shower temp will still fall uncomfortably low before the boiler has a chance to recover. But at least it should come back up, and preempt the heating zones in the meantime.
    It also causes some extra cycling, because if the zones call with the boiler already at temp (and no demand on the domestic), it will quickly drop that heat into the house, and then stop circulating until the boiler comes back up. I don't think this will be a huge deal though.
    Let me know if you can think of any other problems with this approach, otherwise I'll try it for a few days. This could be the motivation I finally need to switch to a heat pump water heater while there are still rebates & tax incentives…
  • LRCCBJ
    If you disconnect T-T, I'm unsure how the zones can call the circulators. Of course the boiler can maintain 180/160 forever but what stops the pumps………….only when they fall below 160? It might get a bit warm in there………………..
  • pedmec
    pedmec Member Posts: 1,460
    your Hydrostat will maintain the minimum temperature needed for the tankless coil to function. it should disconnect the heating circulators when there is a hot water demand. There are other things to check.
    what size tankless coil?
    did you use a mixing valve?
    and if you did, did you set the temperature?
    what temperature is leaving the coil?
    what is your low limit set for?
  • LRCCBJ
    Unfortunately incorrect. When multiple zones call, the Hydrostat has no chance to maintain minimum temperature. The radiation controls that.
    HVACNUT Member Posts: 7,526
    When using a zone panel when the boiler has a tankless coil, ZR,ZC must be used, not XX to TT. This is a line voltage circuit but it's the only way.
    LRCCBJ
  • riny
    No, there's an Argo relay board. What I have now (with only ZR-ZC and no T-T) seems like exactly what I wanted. The Hydrostat always tries to keep the boiler temp between 160-190. Each zone's circulator only runs if the Argo gets the signal from the thermostat and then engages the pump relay. When the boiler temp goes below 160, the Hydrostat breaks the circuit between ZR and ZC, and the Argo doesn't allow any of the zone relays to engage. So in theory, heating demand can never cause the boiler to go below 160, and there will always be hot water available for showers.
    I haven't taken a shower since making this change but in practice, I don't think it's going to work that cleanly. I was watching it today and when the ZR-ZC cuts off at 160, yeah the circulators stop and the burner kicks on, but the boiler temp continues to drop as the heat dissipates, going down to about 130 before the burner has warmed up enough to start raising it. Granted it was a very cold day today. But if you're in the shower when the heat comes on, I predict you'll get a few minutes of lukewarm water and then eventually it will get hot again.
    This must be what led the previous owners to add the indirect tank, which was installed later than the boiler but failed first and had to be removed.
  • bburd
    bburd Member Posts: 1,318
    Many tankless coil systems were traditionally set at a low limit of 180° and a high limit of 200° F. Assuming the tankless coil is clean (not limed up) and there is a low flow showerhead, that should work if the aquastat has good thermal contact and is working properly, wired to act as a circulator/low limit control to maintain boiler temperature. For safety, current codes require a thermostatic mixing valve with this arrangement to reduce the danger of scalding.
    Bburd
  • riny
    Thanks, I do have a thermostatic mixing valve, put in when the tank was removed. That's a good suggestion, if the temp is dropping too low after the stat cuts out, I'll try it with higher limits.
  • LRCCBJ
    It appears you have it setup as best as you can. I am a bit curious why the boiler drops 30F AFTER the circulators stop. The only way that is possible is if the Hydrostat and the temp gauge are in two completely different locations on the boiler and it takes some time to equalize once the circs stop. 30F seems to be a massive differential inside the boiler.
    As you noted, you won't be pleased if the boiler drops to 130F at the point where a shower is demanded. Remember the shower will demand about 100K (80F rise with 2.5 GPM) so you only have about 45K remaining to lift the boiler temperature and all that cast iron. It's going to take a bit of time.
    The higher limits will help but the fuel consumption will climb due to maintaining the LL of 180……….indefinitely.
    EdTheHeaterMan Member Posts: 12,504
    Are there flow control valves on the supply side of each circulator zone? You may be getting gravity flow after the circulators are stopped by the ZC/ZR low limit circuit. That is the only thing I can think of that will allos the boiler temperature to drop after the pumps stop.
    If you do have flo valves on the supply side of the zones, are they all set to the automatic position or are they set to the open position?
    Read this section starting on page 9, of the following book:
    https://s3.amazonaws.com/s3.supplyhouse.com/product_files/108119-Reference%20Guide.pdf
    Flo valves are used for 2 reasons. On single zone systems that have tankless heaters they keep the hot water in the boiler when there are no circulator pumps running.
    On zone systems to keep the water from flowing backwards in the zones that are off.
    Your system uses both reasons because you have zones and a tankless coil.
  • riny
    Yes I just looked up flo-control and I have those valves. Funny, I never knew what they did before! I think I figured out why the boiler temp was dropping so much though, and it was down to a bad test. Rather than running the shower (2 flights up) while I was testing this setup, I turned on the hot water in the basement utility sink. It's right next to the boiler, with a big unrestricted faucet / no aerator, and I opened it all the way up. I think it was this massive flow pulling the heat out of the boiler via the coil that caused it to drop so much before the burner could get it back up. Yesterday and today I made sure to take showers at a time when at least one zone was active, and with a normal demand, the boiler was able to maintain the temperature after the circulators cut off.
    So in the end this was a very simple fix. The service guy hooked the aquastat up to T-T. I wired up ZC-ZR with suitable line-voltage wiring (removing the jumper on the relay panel), removed the T-T connection, and that was all it took. I didn't have to change anything else or adjust the limits of 160-190F.
    Many thanks all for your help!
    bburd