1950’s residential boiler

Riley24
Riley24 Member Posts: 5

I am wondering if anyone knows what these fittings are in the picture? They are on the return side of my boiler. And is it possible that they can get clogged up, not pass water through.

Comments

  • Steamhead
    Steamhead Member Posts: 17,410

    Balancing valves. You can adjust them to make sure the system heats evenly. If the system already heats evenly, they're fine.

    The one looks like the packing might be loose.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Riley24
    Riley24 Member Posts: 5

    thanks for the info, the valve in the background is from my living room and kitchen which do not put out hardly any heat, when I bleed register only ambient temperature water comes out, is it possible that balancing valve is clogged or needs adjustment?

  • bburd
    bburd Member Posts: 1,058

    That type of balancing valve usually has a screwdriver slot inside the nut. When the slot is parallel to the pipe, the valve is open; when it is perpendicular to the pipe, the valve is closed. A 90° turn adjusts from fully open to fully closed. You may need to loosen the nut to turn the screw. Snug it back up, but not too tight.


    Bburd
  • Riley24
    Riley24 Member Posts: 5

    thanks, what I don’t understand is the valve that appears to be in the on position is the heating circuit that is putting out no heat, it’s like that pipe is clogged or that valve is bad?

  • bburd
    bburd Member Posts: 1,058

    What is happening on the supply side? Circulator running normally? Zone valves open? How far does heat move up the pipe?


    Bburd
  • hot_rod
    hot_rod Member Posts: 23,507

    it is rare to see a valve like that suddenly fail closed . An air pocket of failed pump is a more likely condition

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2Long Beach Ed
  • Intplm.
    Intplm. Member Posts: 2,217

    @Riley24 Please post a few more pictures. A close front, view of those valves and some pics farther away as best you can. Those valves could also be part of a purge valve system. Give us a better look.

  • Riley24
    Riley24 Member Posts: 5

    the heating circuit in question the pipe is hot to the supply side of the register, when i bleed out that same register only cool water comes out, it goes through 2 more registers that have auto bleeders installed and comes back on the right side pipe in the picture! Only 1 circulating pump.

  • mattmia2
    mattmia2 Member Posts: 11,029

    The one on the left should be mostly closed, the one on the right should be fully open.

  • Riley24
    Riley24 Member Posts: 5

    yes that’s the way I interpret them valves, it acts like that whole heating circuit, that’s the valve with the green crust on it, is clogged! No water flow, that’s why when I bleed the register in my living room the water is cool? I appreciate the help!