Honeywell gas valve spark ignition problem

Crown Aruba AWR 38. Error 4 occurs after gas valve is open for five minutes or so, with 24 V to the PV and also the MV. my milliamp on the control board will start to drop down from 15 mA and linger around four or 5 mA until it goes further down to shut the gas valve. Then it goes into a restart and the process continues. ending with an error code 63 soft lockout. The pilot assembly with flame sensor spark igniter has been replaced. inlet gas pressure is 7 inches water column and downstream pressure is 3 inches water column. Burner flame tubes fire is not drop down as the pilot flame diminishes.
It is as if the pilot solenoid is closing on its own while 24 V remains at the gas terminal. Any help would be appreciated thanks.
Comments
-
Hello joebark,
Sounds like you went through the list below. I'm not clear on one point in your description;
" my milliamp on the control board will start to drop down from 15 mA and linger around four or 5 mA until it goes further down to shut the gas valve."
" Burner flame tubes fire is not drop down as the pilot flame diminishes. "
While you see the current diminishing from 15 microamps to less than 4 or 5 microamps is the pilot flame diminishing during that time span too ? Or does the pilot flame go from normal to extinguished almost instantly.
If the pilot flame diminishes as the current drops, I would probably want to monitor the gas pressure in the pilot tubing circuit to get a better understanding of what is actually happening. A special adapter may have to be fabricated if there is no test port for the pilot on the gas valve.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Thanks for the reply. Yes as the mA starts to drop the pilot flame size is also dropping. Flame at the burner tubes are still perfect. I believe the controller is reading the pilot flame accurately. I'm wondering if anyone has seen the pv solenoid slowly close while 25v is present?
0 -
Down stream gas pressure should be 3.5 in wc may at least help, I would raise it and re test.
Robert W.
Energy Kinetics
0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements