Honeywell gas valve spark ignition problem

joebark
joebark Member Posts: 4

Crown Aruba AWR 38. Error 4 occurs after gas valve is open for five minutes or so, with 24 V to the PV and also the MV. my milliamp on the control board will start to drop down from 15 mA and linger around four or 5 mA until it goes further down to shut the gas valve. Then it goes into a restart and the process continues. ending with an error code 63 soft lockout. The pilot assembly with flame sensor spark igniter has been replaced. inlet gas pressure is 7 inches water column and downstream pressure is 3 inches water column. Burner flame tubes fire is not drop down as the pilot flame diminishes.

It is as if the pilot solenoid is closing on its own while 24 V remains at the gas terminal. Any help would be appreciated thanks.

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • 109A_5
    109A_5 Member Posts: 2,375

    Hello joebark,

    Sounds like you went through the list below. I'm not clear on one point in your description;

    " my milliamp on the control board will start to drop down from 15 mA and linger around four or 5 mA until it goes further down to shut the gas valve."

    " Burner flame tubes fire is not drop down as the pilot flame diminishes. "

    While you see the current diminishing from 15 microamps to less than 4 or 5 microamps is the pilot flame diminishing during that time span too ? Or does the pilot flame go from normal to extinguished almost instantly.

    If the pilot flame diminishes as the current drops, I would probably want to monitor the gas pressure in the pilot tubing circuit to get a better understanding of what is actually happening. A special adapter may have to be fabricated if there is no test port for the pilot on the gas valve.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • joebark
    joebark Member Posts: 4

    Thanks for the reply. Yes as the mA starts to drop the pilot flame size is also dropping. Flame at the burner tubes are still perfect. I believe the controller is reading the pilot flame accurately. I'm wondering if anyone has seen the pv solenoid slowly close while 25v is present?

  • Robertw
    Robertw Member Posts: 46

    Down stream gas pressure should be 3.5 in wc may at least help, I would raise it and re test.

    Robert W.

    Energy Kinetics