Inducer Motor Replacement Bryan 90 Plus

I have a Bryan 90 Plus furnace that needs the inducer motor changed. The company that came to look at it wanted $1200. I googled and found that it was an easy job. I ordered what I thought was the right part. Everything fit exactly as it should. The only problem was my wire connection has 4 wires and the new one has 3. Is there a fix or can some point me in the right direction to the correct part?
Comments
-
I don't know. You should only need 3 wires to run the inducer, hot-Black, neutral-White and green-Equipment ground.
Maybe the 4th wire coming out of the motor is a centrifugal switch output to prove motor operation.
Is there a pressure switch installed on the furnace to prove the inducer is running?
Look at the manual & the original wiring diagram and find out what the 4th wire does will give you a clue
Maybe you could provide model # and serial # so it can be looked up.
0 -
-
-
-
JE1D017
0 -
-
The old inducer motor part number that starts with HC27 AND the furnace model number . I can look it up on the Bryant Dealer website. There may be a new number for the part that says "Replaces HC27?????"
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements