The Tankless Paradigm w/"Virtual Storage Tank"?
Comments
-
@RickDelta : "Lets take a single 199K tankless unit and set the tankless set temp to
185 degrees F.
(@ a max 3 gpm flow demand )Run its output into a mixer valve (its out temp set to
125 degrees F
)Roughly, doesn't this
significantly increase
thetotal available (mixed) hot water
capacity (@125 degrees F)
over just the single tankless unit at its max flow rate of 3 gpm ?"This is where your conceptual flaw is. It doesn't increase the total available hot water capacity one bit. This is what several people have been trying to tell you, you keep insisting we don't understand what you're trying to do.
Look at the chart 199Delta.png that you posted. It's right there.
0 -
If the Rinnais are keeping their internal buffer tanks at 180, and you are mixing down to 120, here is a calculator from the Lochinvar Tool Kit to calculate additional capacity. I assumed 30 gallons each in the Rinnais? 60F inlet water temperature?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
With any public use building you really want to have a listed mixing valve that data logs it's temperature condition. Tie it into the BMS also, to log that data.
We had a LegoMix installed at a correction facility. It logs 40 days worth of information.
An inmate tried to sue claiming he was scalded in the shower. The building operator was able to pull the data for that day and time and show the valve never exceeded 120F at any point. Case dismissed.
Liability becomes more of an issue than accurate , for the valve manufacturer and building owner, vs temperature regulation, unfortunately.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream4
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 101 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 934 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements