Newly refilled hydronic system- proper max pressure
our boiler sprang a leak Saturday night
It can just be made out along that pale red line across the center of the photo above. With enough water drained from the boiler(not much) the pressure dropped to zero and the leak stopped. It had been leaking ~1/2 g/hr at the end of the day Monday. We were fortunate to be able to collect the water in an oil change pan and using a thirty mate bilge bump get it into a buckets to dump. After two days of refilling with the auto fill there was much entrapped air in the system at bedtime Monday night so I shut it down. Today Iran a hose from the boiler drain outside and drew off a tiny bit of water. After it dried out I hit it with the wire wheel real
well, scrubbed it clean with Acetone on a rag till the rag came out clean, and applied this stuff.
This ain’t Grampa’s J-B Weld.
this was the result and 4 hours later I flushed the air out of the system as per many descriptions on this site and elsewhere. Let the auto valve fill to what appeared on the gauge to be 12 psi. Opened all the appropriate valves and fired the burner. The boiler had been off for ~18hrs so was lukewarm warm. Didn’t time how long it ran but it came up to temp and the pressure rose to 28 lbs. 25 year old gauge, so who knows. It is short cycling as the house is rewarming and demand is constant. We are way over boilered I know. Long story. The replacement due shortly is properly sized.(Better anyway).
Regarding the pressure, it filled to 12 psi cold. With the boiler now up to temp it is hovering between 22 and 28 as it cycles. No ominous signs from the 30 psi blowoff valve. So, all good? Seems like we’re living on the edge here. My first forced ghetto fix on a boiler which I see everywhere is doomed in short order. But it’s a fun experiment as long as it’s safe, it appears to be working and I will shut in down at bedtime again regardless. My heat contractor is distracted by a sudden family illness so I’m not bugging him and I need tokeep warm. I have a great working woodstove we haven’t use in years. There’s always that. But I have a 1200 ft slab on the first floor to heat that part of the house so I’m trying to keep that warmed up. Hopefully the ship will stay afloat for a couple more days till the deed gets done. 🤞
This is the repair 1 hour after firing off. There is a slight damp spot at the left hand side. Doesn’t drip, just gets wet then dries during off cycle. So far so good. Sorry for the long windedness, a trademark I’m afraid. Any thought on the pressure would be welcomed and greatly appreciated. Thanks to all. Best wishes with all your projects.
Comments
-
Normal pressure is 12-15 with a cold boiler. When it is as hot as it gets you should be 20-22 at the most. 12-15 is enough pressure for a 2 story house. You need roughly 1 psi for every 2' of rise from the boiler to the top of the system plus 5 psi. So for 40' height you would need 25psi.
Either your PRV is not adjusted right ….leaking by or your expansion tank has failed or is water logged.
With the patch I would measure the height from the basement floor to the highest part of the system. Divide that # by 2.31 and add 5 psi to that.
With the patch I would run the lowest pressure you can run. You might get away with less than 12-15 if your house is lower than 2 stories.
1 -
I found the Watts document on servicing the SB1156F auto fill valve
my question is, when I go through the process of lowering the set pressure, (tag shows 10psi min), how does the excess pressure get relieved? Will I need to connect a hose to the boiler drain and bleed off some amount of water? I see no way for the pressure to simply drop. It can’t relieve itself back through the valve against 65 lb water system pressure…correct?
Pressure was at 15psi cold this am when I fired the boiler. It rose to 25psi at 190deg high limit shut off, then slowly dropped during off cycle. As it had done last night so all seems steady/predictable at this point. I have a 10’ rise to top of system so absolute min pressure would be ideal for preservation of my band aid. So far so good but I’ve not heard from my contractor and this fix MUST last.
Thanks folks for your kind input, it’s much appreciated by the anxious homeowners.
0 -
That increase in pressure is an indication of not enough room for expansion. The expansion tank might have failed or needs to be recharged with air. You will need to isolate the expansion tank and drain the boiler pressure from it. With zero water pressure on the boiler you set the air bladder charge to the fill valve pressure. Typically 12-15 PSI for a two story home.
0 -
thanks super tech. I’ll see if I can get the contractor out here to just do that particular tune up just to help get us to the main event.
0 -
the new boiler got installed today.
All seems well, to a point. The radiant floor mixing valve appears to not be operating correctly.
after the initial firing the tech was observing everything carefully, opening the loops individually and feeling the return lines. Was looking over the radiant manifold and fussing around when a white pill shaped object fell to the floor. “S***, grab that” (to his partner) as I squawked “what are you doing?” Checking to make sure it’s moving. He could have asked, the system works fine and adjusts system water temp vs outdoor temp beautifully. I had moved the setting up in recent days to heat the slab a bit more since I was shutting the boiler off at night so’s not to worry about the leak. So I had the temp varying from 90-120 and finally backdown to 90 deg. All good. Now after putting the Oventrop outside setback temp controller back together on the mixing valve there is 145 degree water running into the supply side of the radiant manifold. I’ve turned the controller off (dial down to ❄️), yes, that is the lowest setting, Even in the off position the valve is evidently diverting most of the return water back to the boiler and allowing way too much hot water into the system. I had slab temps up to 96deg and finally turned off the radiant circulator off and closed the valves to the manifold. I will contact the contractor tomorrow to sort this out but I was wondering if anyone here have experience with this type of temp controller and know what may have gone wrong when things fell apart. As always thanks and best wishes.
0 -
A few bummers. I think the boiler pump is on the return pumping at the expansion tank. A low performance air purger, maybe not enough horizontal run upstream.
The low temperature flow usually pumps away from the mix valve. It pulls from the h and c port to mix. I think the circ is pumping into the valve? If the sensor is on the supply manifold. Would need to see the installation sheet for that valve.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Indeed the circulator is on the return, as was the setup on the old Boiler. Seems to be the norm in our neck of the woods. I did note the air scoop was of a smaller size than the previous installation. As to the horizontal run, I assume you’re referring to the supply line out of the boiler, I can’t speak to that as I know nothing of what that should be or why it’s inadequate in your view.
As to the radiant manifold itself, in 1999 I guess that was the accepted practice. It’s worked flawlessly til today. Shows what I know and I didn’t do either install. It should be noted that the whole manifold/circulator/ mixing valve / shutoff valves came as an assembly from Stadler and the installer simply tied it in.
I guess the tech had unscrewed that white cylinder beneath the mixing valve and that pill thing was some internal part to that. I haven’t found a parts schematic for the Oventrop controller and I doubt I will.0 -
Oventrop pulled their office out of the U.S. maybe find some legacy documents on their main site.
If it worked in the past, hopefully you can sort it out.
I believe it is a wax motor type of control, a small copper “pill” or capsule under the white cap, with a remote sensor
The workmanship look nice.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements