Navien NFB boiler zones.

Hi Guys

is there any cheaper way to control more than 3 zone pumps with the Navien NFB boiler than buying ther extra zone controller add on which seems expensive as i just need 1 extra zone, total 4?

thanks

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,388

    Maybe but we would have to know how the boiler is piped. Do you have primary secondary piping or straight through piping? and do you have a boiler model # and /or wiring diagram you can post.

    Pictures will help.

  • JMWHVAC
    JMWHVAC Member Posts: 56

    Any circulator zone panel will do. But it will wire to one of the navien zones so you need a minimum of a two zone control panel. Those NFB are good boilers.

    GGross