I have an old 195k btu input American Standard boiler. Model GPM-7. Cast iron heat exchanger, cast iron burners. VR8304 gas valve adjusted to 3.5 in w.c.
I rented a testo 300 to perform a combustion analysis on it to see how it was performing and am a bit perplexed by the results.
O2, CO2, and CO all look ok to my eye, but the T-stack temperature looks high. 550-575F. I expected it to be 450-475F
Also CO seemed to improve a bit with the vestibule cover in place. Not sure what that indicates.
Is this temperature too high? Any place to start looking for issues? I had brushed out the heat exchanger earlier in the fall and it looks pretty clean.
Your #s for that boiler look pretty good to me. In fact I used to have that same boiler but with less sections and lower BTUs. It probably dates to the late 60s-early 70s.
I changed the boiler when I sold my house a few years back although it ran fine because the new owners wouldn't bite on a 40-50 year old boiler.
Keep in mind that your basement ambient temperature is usually deducted from the actual stack temperature to get the "net stack temperature" so that would give you a net stack temp of 499 or so.
I don't know if the TESTO 300 does this deduction automatically for you or not' You could take the actual stack temp with a thermometer to figure this out.
1 -
I agree with @EBEBRATT-Ed - those are good numbers for a 1960s boiler. Fuel was cheap back then. There wasn't much incentive to make them efficient. Also, the sections in GPM boilers are stacked vertically, and I don't think they had baffles, so the GPM is pretty much "up and out". That helps account for the stack temp.
Consulting1 -
Burners are clean and the draft was .08 in wc. Readings were taken after running for about 20-30 minutes and were steady.
@Steamhead is right the sections are stacked vertically and there are no baffles.
If 575 F isn't concerning for the Stack temperature, I'll let it keep soldiering on. Thanks all.
1 -
-.08 is some pretty good draft. Like doubly good. Not much to do about it without replacing the flue.
You're a little high with your O2 but that is most likely related to the high draft which would account for a higher flue gas temperature. The excess O2 is "just passing by" and stealing some of the heat with it. Other than that very minor issue I would leave it as is because safety comes before efficiency and trying to tweek it might cause your CO to spike.
1 -
so the scale was cleaned on the fire side of the chambers, don't forget scale on the water side can also hinder heat transfer.