Three years ago a friend and I installed a low temp gas fired radiant heating system for my staple up and radiator style heating. At that time I elected to incorporate some glycol from sentinel, but I think I underestimated the amount I needed to get at least 15-20%. Since the install, I’ve noticed that some of my connections have slight weeping and a concentration test shows. I’m sitting around 10% glycol. I can see there are some lines that have either sediment or some type of growth in them and I’m wondering if I need to do a system flush and refill.
I originally wanted some glycol due to the corrosion, inhibition properties and freeze protection. I don’t think the freeze protection is absolutely necessary unless I were to have a power failure for several days, but at that point, I probably have bigger problems than just my radiant system.
At this point, what do you guys think I should do? Drain and refill? Top off with more glycol?
Part of me would like to go to 100% water for simplicity but I know it will be challenging to properly flush all the lines.
Boiler is a Weil Mclain evergreen. Steel radiators, staple up, uponor pex.
Comments
-
Glycol only if absolutely necessary. 30% is about as low as you want to mix, according to the manufacturers. The inhibitor that protect the metals are too weak below that. Including anti bacteria protection. That will take a few days of running all the zones to get all the gunk out.
Fernox, Rhomar, Adey, Hercules and others have hydronic cleaner.
Flush it, run a cleaner, flush again, add water that meets the Weil spec. Test your on site water to see how it compares.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
thank you!
0 -
I like to use a hydronic conditioner. It protects the equipment and balances ph.
Unless you have the exact hardness and chloride and TDS you are just guessing. It's rare to have well water below 7 gpg. A test kit for hardness is around 30 bucks. TDS stick meters under 100 bucks. Or find a water treatment company to test your water.
If any of those numbers are out of range you can buy a basic one time deionizer, or by water to blend with your well water to get it in spec.
If you live in an area where they use deicers on the highways, you may have high chloride levels. Wells along interstates are see 300ppm chloride levels!
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Thank you once again!
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements