Rinnai will not ignite

New installed Rinnai i060 wont ignite, LP gas is to the unit and conversion is intalled, water pressure is good, igniter appears to be working, but the unit wont fire when heat is called for. Any ideas?

Thanks

Comments

  • Big Ed_4
    Big Ed_4 Member Posts: 3,112

    My first thoughts gas pressures and adjustments . What are they ?

    There was an error rendering this rich post.

    Intplm.
  • Slimpickins
    Slimpickins Member Posts: 353

    First of all, make sure you have an LP boiler. Don't laugh, it happens a lot, especially if you're getting them from online suppliers. If not, no big deal, just get a conversion kit. It's no big deal to convert, just replace the blue, NG orifice with a red one and change parameter AO to LP. Don't make any adjustments on the gas valve, everything is ready to go right from the factory. Make sure your incoming gas press doesn't drop below 8"w.c. during ignition attempts and sure be no higher than 13.5"w.c.

    Is this a new LP tank? Rinnai boilers, even with the best-purged tanks, can sometimes be a problem during the first few ignition cycles. Try covering half the air intake horn with some duct tape. That's the black tube on the bottom of the gas valve. If it fires up, leave the tape on for the first full week of operation.

    Intplm.
  • Josh10mm
    Josh10mm Member Posts: 3

    It is a new tank, and the LP conversion is installed, the regulator is set for 11" w.c., though I am not equipped to verify that. I havent done anything with the gas valve, I dont think its adjustable anyway.

    I'll try the air intake idea and see what happens.

  • Josh10mm
    Josh10mm Member Posts: 3

    update: tape on the air intake worked. It fired up right away.

    Thank you!