Alta 120 settings
We put in one zone, has 3 loops, of staple up radiant heat running with the aluminum strip to spread the heat. We have plans to add two more zones, but wanted to tie it all in and test it before moving on to the next zone.
My question is about the settings on the Alta-120 boiler. We have it set to 120° on CH1 & CH2, and we aren't using it for DWH at this time but have a 110° set there as it seemed to want something. The boiler comes on and starts heating fast and zips up to about 145 and then backs off fast enough to get a H01 error code.
I am not sure what setting we have wrong that is doing this. Any ideas on troubleshooting this one??
CPowell
Show us how it's piped. If it's not primary/secondary with appropriately sized circulators, that's your problem. If it is P/S with appropriately sized circs, it's either low on pressure or airlocked. WHat is the system pressure and how did you purge the radiant loops?
We will give that another round to see if we can bleed off more air. We have a plan for the condensate drain, just hadn't gotten there yet. Wanted to test everything before it gets super cold up here!!
Thank you for the suggestions, we will also check that history log to be sure there isn't something else to work on. So you think the settings might be fine? Still just air?
CPowell
The error implies an issue related to the system and not settings in my opinion. The boiler overshooting the target temperature very quickly implies a lack of heat transfer, probably due to lack of flow cause by air in the heat exchanger.
@clpowell72 , did you figure out what the issue was? Curious because I have an Alta 150 that has the same problem - heats up to ~170 very quickly and then backs off fast enough to throw a H01 anti-short cycle code. I have hydro-air and I get this code typically on a cold start. When pipes are hot, it doesn't happen as much.
- 125 Chimneys & Flues
- 19 Recall Announcements
