Laars FT series Boiler
just install a Laars condensing boiler replacing a traditional casts iron boiler with Slant Fin baseboard throughout the house. Should I use the outdoor reset sensor or leave steady 180 to baseboard. With late fall temps I run about 135 degree water on the sensor. Maintains the house but not sure if it’s the most efficient way to go running low temps through the old baseboard
Comments
-
ODR will always offer a fuel savings. Even with that so called "High Temperature" baseboard. You will get more efficient operation is the spring and fall months with the lower temperature water running thru those copper veins and arteries. You now have a great heart connected to them.
Diagnosis by EdTheHeaterDoc. LOL
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements