Gravity system. "No Heat" call. At first I thought it was a bad thermocouple; only getting 9 millivolts. But it still wouldn't fire with a new one. The aquastat is fine. I'll change the gas valve.

Any idea what the input rating is? 200K?

8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

Two btu per sq ft for degree difference for a slab
PC7060delcrossv

Comments

  • mattmia2
    mattmia2 Member Posts: 11,085
    edited October 2024

    you need a professional that understands conversion burners and combustion to adjust ne new valve if you replace it. did you press the reset button on the baso valve after you replaced the thermocouple? did you check that there is power from the transformer and the thermostat was closing?

    EDIT:
    I didn't see who posted this. the input would have been set while setting up the combustion by looking at the stack temp and the water temp.

  • Larry Weingarten
    Larry Weingarten Member Posts: 3,628

    Nice find! I really like the knurled thumb and flat screwdriver screws on the aquastat. We don't make em like that anymore. 😇

    Yours, Larry

    Alan (California Radiant) Forbes
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,719

    oldie for sure.

  • Steamhead
    Steamhead Member Posts: 17,461

    In the 1913 "Ideal Fitter", that boiler is rated 500 square feet of hot-water radiation on coal. At 150 BTU/square foot, that works out to 75,000 BTU per hour (75 MBH). For comparison, a Peerless EC-03 boiler has a net water rating of 80 MBH, and fires at 0.75 GPH or 105 MBH.

    Since an old coal boiler like that might be as low as 50% efficient, especially if the flue passages are not baffled, firing it with an input of 150-200 MBH might not be out of the question. You'd basically have to try it and see, using the analyzer of course.

    I'd at least get that customer to consider replacing that beast. Yes, I know that would cost big bucks, but the fuel savings would probably make the job worth it.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Alan (California Radiant) Forbes
  • tim smith
    tim smith Member Posts: 2,807

    Alan, it’s probably a bad Basi pilot safety, one with red button. How many mv you getting at baso with thermocouple screwed in with test jack inline? The little magnet wires in baso break eventually. You can get a new inline pilot safet valve. I am pretty sure I have one on shelf.

    mattmia2
  • tim smith
    tim smith Member Posts: 2,807

    test outlet pressure tap to main gas valve for pressure when pilot lit and baso reset. I main valve opening? But no gas?

  • @Steamhead I've been working with the five children who grew up in this house. Their parents are still living there, but they are not in good shape and the kids are making sure that they are comfortable and have everything they need. In the meantime, they don't want to make any major changes.

    @tim smith I'm pretty sure you're right about the Baso safety. You can feel the magnet hold the valve open when you push and release the reset and that wasn't happening here, even with the new thermocouple. But I didn't trust the Honeywell main valve as it was getting very hot on a call for heat.

    So, I'll be installing a new combination gas valve and aquastat. When I drained the system and started unscrewing the old aquastat after the system had fully drained, I noticed air being sucked in through the threads of the aquastat and more water draining out of the system; a lot of water over an hour or so. I thought to myself, how can this be happening on a vented system. I found the reason, not in the attic, but hidden in the shadows against the wall between the boiler and the water heater. Any guesses?

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • mattmia2
    mattmia2 Member Posts: 11,085

    Sidearm water heater.

    You could check the coil on the baso with an ohmmeter, it is just a solenoid powered by the thermocouple.

  • 8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    mattmia2PC7060
  • mattmia2
    mattmia2 Member Posts: 11,085

    oh, a heat generator

  • RayWohlfarth
    RayWohlfarth Member Posts: 1,665

    Wow nice system

    Ray Wohlfarth
    Boiler Lessons
  • I thought it was so cool that Rubbermaid came out with an attic expansion tank replacement.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    PC7060SunRad