Pump recommendation?
HeatingHelp
HeatingHelp Administrator Posts: 727
This discussion was created from comments split from: best pump for hot water loop.
  • Newjersey_Scot
    Newjersey_Scot Member Posts: 2
    @EzzyT - I currently have a B&G NRF-22 and have had taco pumps of similar size but they keep breaking due to dirt water as part of a hot water loop off a single pipe steam radiator boiler. The boiler is due for replacement soon but trying to delay till after this winter. I saw you mention a 3 piece pump would you recommend one of the below or something different? https://www.supplyhouse.com/Bell-Gossett-106197LF-1-12-HP-Series-100-Bronze-BNFI-Circulator-Pump
    https://www.supplyhouse.com/Bell-Gossett-106192LF-1-12-HP-Series-100-AB-Bronze-Circulator-Pump
    https://www.supplyhouse.com/Bell-Gossett-1BL013LF-PL-30B-1-12-HP-Bronze-Booster-Pump-Lead-Free
    Any concerns if the pipe work doesn't include a wye strainer? Any other recommendations?
  • HeatingHelp.com
    HeatingHelp.com Member, Moderator, Administrator Posts: 250
    @Newjersey_Scot, I've created a new discussion for you here so that your post doesn't get lost at the bottom of an older discussion. Welcome to Heating Help!
    Forum Moderator
    hot_rod Member Posts: 27,792
    Do you know the gpm requirement? The B&G PL series has a separate motor, not water lubricated. It is less $$ compared to the series 100. Cast iron will be less $$ also.
    EdTheHeaterMan Member Posts: 12,486
    You might want look into getting a tankless coil for your new boiler. The tankless coil will separate the boiler water/condensate from the circulated water. I have used this on a church that has a 2million BTU boiler that needed to make steam for 3 offices and 2 bathrooms when the Sanctuary and/or Hall was not in use. That got expensive.
    By removing the steam rads form those rooms, and putting in about 30 feet of baseboard connected to the tankless coil, the boiler only needed to get the water to 150°F to heat that small zone. The coil was set up with an expansion tank, relief valve, air purger, circulator and fill valve setup. Worked like a charm.
    As far as your current problem is concerned, You might want to use a lower cost pump if ypu are going to be swapping that boiler in the near future. If you are like me though, you may never get to that new boiler, so you might as well get the bronze B&G 100. $$$$$$
    Newjersey_Scot
  • EzzyT
    EzzyT Member Posts: 1,380
    bronze 3 piece oil lubricated pump like a B&G 100 is what you’ll need.
    But as @EdTheHeaterMan has mentioned when the boiler get replaced go with a tankless cooler for that zone.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
    Newjersey_Scot
  • Newjersey_Scot
    Thanks!! Is there much difference between the Bronze BNFI and the bronze AB pumps? Good to know on the tankless option for the future.