Rinnai i-series issue

2drgns
2drgns Member Posts: 3

I have an i-series solo boiler, it's setting heat chamber over heat error code. It seems like the circulation pump isn't kicking on at all. It works when hooked to outside power source. The zone pumps work also. I tried the de-airation mode and only one zone pump cycles, the other or main pump doesn't. Any ideas on what to check next????

Comments

  • hilltown
    hilltown Member Posts: 28

    with a multimeter checking voltage to the circulator from the pc board when a call for heat or indirect is on.

  • 2drgns
    2drgns Member Posts: 3

    I checked all. The main and one zone have power reading 1 terminal, 2 ND zone has power reading both terminal and pump running.

  • 2drgns
    2drgns Member Posts: 3

    Putting power to main pump directly the boiler runs perfectly, less the one zone pump or main pump terminals not energized. I'm kinda leaning toward bad PC board...