Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
purge light flashing CGI 8 NG
rbkerrigan
Member Posts: 1
I have a 12-year-old Weil Mclain NG CGI 8 boiler. The boiler fires up and runs for about 1 min and then turns off with the purge light flashing.
- I checked for any blockages in the vent, it was clear.
- I replaced the pressure switch, but the problem continued.
- I bypassed the pressure switch and then the boiler operated normally.
- The fan motor sounds ok.
Follow up:
I CLEANED THE PORTS THAT THE PRESSURE SWITCH HOSES ATTACH TO. THAT SEEMS TO HAVE DONE THE TRICK. MAYBE A WEAK BLOWER FAN TOO. WE WILL SEE.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements