Argo AR861-211 two zone issues.
I am new to this forum and new to heating issues. I have read most all of the postings on this unit but I would like a bit clearing up. To make sure I understand correctly. Have had no issues with this unit for over 15 years.
At start up this week. Neither thermostat turned on either pump to zone on or 2. I have checked all the relays. They seem fine. I have jumped a wire over both stat terminals and still nothing happens. Am I missing something else to test or do I need a new board?
Will attach photo asap.
Again. New to all this so may not understand all the lingo. Appreciate your time.
Comments
-
0
-
Do you have 110 volt power coming to the control?
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Yes, 110 Power to the control.
0 -
A wire Jumping T1T1 should turn on zone one. Priority switch is on, so only zone 1 will activate while it has a call for heat.
0 -
Jumping T1T1 does nothing.
0 -
The transformer may have blown or the circuit board is history. Time to replace it.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Thanks Alan.. That is what I am thinking.. Just wanted to be sure.
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements