Tiger loop installation

ksk
ksk Member Posts: 7

2 seperate tiger loop , 1 for each burner installed. Using original inlet on side of pump with return on bottom. Is this ok rather than the inlet/ outlets both on bottom of pump?

IMG_6696.jpeg IMG_6697.jpeg

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • HVACNUT
    HVACNUT Member Posts: 6,769

    That's fine, as long as the Bypass plug is in on both.

    I like to use a short 1/4" nipple and elbow out of the bottom, and make the connection on the horizontal so I can get a tray under the pump to catch the oil when I take off the pump cover.

  • Big Ed_4
    Big Ed_4 Member Posts: 3,205
    edited September 2024

    You sill need a Fire-o-matic valve at the pump.. I would switch to the inline type using the bottom taps …

    There was an error rendering this rich post.

  • Grallert
    Grallert Member Posts: 965

    👍️

    Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,799

    Looks like they have firomatics at the pumps looks ok to me.