Tiger loop installation
ksk
Member Posts: 7
in Oil Heating
2 seperate tiger loop , 1 for each burner installed. Using original inlet on side of pump with return on bottom. Is this ok rather than the inlet/ outlets both on bottom of pump?
0
Comments
-
That's fine, as long as the Bypass plug is in on both.
I like to use a short 1/4" nipple and elbow out of the bottom, and make the connection on the horizontal so I can get a tray under the pump to catch the oil when I take off the pump cover.
0 -
You sill need a Fire-o-matic valve at the pump.. I would switch to the inline type using the bottom taps …
There was an error rendering this rich post.
0 -
👍️
Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver
0 -
Looks like they have firomatics at the pumps looks ok to me.