Throttling faucet makes water cloudy
I've got a small faucet on my kitchen sink plumbed into a water filter. It's just a carbon filter.
If I run it fast the water is crystal clear but if I run it slow, so you can hear the valve sing the water becomes cloudy but clears up if you let it sit for a short time.
I assume this is air? But from where there's no aerator? Curious what exactly is going on.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Comments
-
-
Boyle's Law of dissolved gasses will explain this.
With the change of pressure happening at the valve when it is partially closed, the water pressure is rapidly dropping at that point whar the water exits the pressurized piping system. That location is where the pressure drop allows the dissolved gasses to exit and form micro bubbles in the water in the glass.
When the valve is full open, the pressure drop happens further inside the piping system (maybe near the filter) causing the micro bubbles to be released before they reach the glass. Those micro bubbles can connect with other micro bubbles to become larger bubbles that exit the water more rapidly when the water exits the valve.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
2 -
Cavitation is another possibility. As flow is restricted
through a valve, pipe, any device you can get vapor pockets forming. Usually there is a noise is associated with cavitation.
It can happen in a restriction, across a rough surface, at your garden hose nozzle, or on the blades of a propeller.
If it is entrained air in the water supply, and there is in public water supplies, it comes out of solution as the pressure is lowered on the water, like when the faucet is opened. If you water pressure is 60 psi, as soon as a faucet opens thatn pressure is released and the bubbles come out of solution.
Any idea of what your water pressure is?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
It's 88-90 before my prv and then 60ish.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements