Need help with eddy system steam boiler.

brklynzoo07
brklynzoo07 Member Posts: 3

I sold a steam boiler job in a very old historical house thinking it was just a typical steam boiler swap out. We'll I get here and start noticing weird things and found out it a vacuum style system called, the eddy system, atleast I believe. But im just wondering if it will still work ok if I swap just the unit out with a new steam boiler and leave the piping all the same. If some one reaches put and knows about this, I have more details. Thanks in advance. Hope someone can chime In on it.

Mad Dog_2

Comments

  • You will have to post some pictures of the existing near-boiler piping before we can comment.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    Mad Dog_2
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,081

    I sorts of do need to offer some constructive criticism. Never ever take any boiler job without seeing it first. I do got to ask. If you didn't see it first, how did you size the boiler?

    KC_Jones
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,081

    And we need to take one step back. A straight boiler swap out, can only work, if previous boiler piping is matched perfectly, and previous boiler piping was relatively perfect, and system function properly. Replacing same for same, it's not necessarily the right way to do things.

    Mad Dog_2
  • KC_Jones
    KC_Jones Member Posts: 5,756

    x2 on this. And since it's a vacuum/vapor system, the boiler sizing is going to be especially critical.

    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    Mad Dog_2
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,339

    Let's go..pictures well get you through it. This is how u learn The Steam . Mad Dog

    STEAM DOCTORAlan (California Radiant) ForbesLong Beach Ed
  • brklynzoo07
    brklynzoo07 Member Posts: 3
    edited June 4

    @steamdoctor I will get some pics tomorrow. But yes, I did see the job before qouting it. But it really just looked like a traditional steam boiler at first. The only thing I missed and didn't notice for some reason, was the radiator didn't have a vent, they have a small pipe running down about ⅜" instead of vent. Reason I didn't notice is because they had covers on them. Also, they went down into the basement into what looks like an expansion tank. Which was kind of tucked away too. Only reason I noticed was because the homeowner pointed it out and asked what it was. At first I told him an expansion tank but I had no clue why a steam boiler would have one. So I researched myself and found it was a vacuum system. Which I've never heard of. Besides that, everything else looks exactly the same as a traditional stream boiler.

    Mad Dog_2
  • Steamhead
    Steamhead Member Posts: 17,130

    @brklynzoo07 , the Eddy System is covered in chapter 15 of @DanHolohan 's book "The Lost Art of Steam Heating". Do you have a copy? If not you can get it here:

    https://www.heatinghelp.com/store/category/steam-heating-books/

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,339

    Yes...If you're going to tackle this job, which you should, you MUST purchase & read Lost Art...Mad Dog

    bburdLong Beach Ed