A little advice
I have the chance to either leave this as is or make some changes I just removed a WM EG-45 and I'm replacing with a W GSA-125 after measuring the radiators, here are some pictures of my setup. I think I need to make some changes.
Comments
-
Just follow what the boiler mfg recommends. They want a 2 1/2" riser out of the boiler and a 2 1/2" header. The existing tee you have can remain as long as the inlet at the bottom is at least 2 1/2" if it is smaller than 2 1/2" change the bushing
Or you can get rid of the tee and drop both supplies down into the header keep them the same size as they are with no reduction.
Do not come out of the boiler tapping and go into the tee without making a proper header that will never work and be a big mistake.
Just follow the mfg. instructions for the piping and the equalizer.
0 -
Ok so I'll remove that tee and call it a day
Thank You.
0 -
I don't like the looks of that tee. Leaving it there makes is look like an amateur didn't know what they were doing. Even if it works, it still looks bad, and your name is on that thing for many years. Something like this would look much better. And it will work great too.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
3 -
I will be pouring a concrete pad today because the floor is not level and when I removed the pipes the boiler was rocking a bit. After that I will start piping.
Thank You.
0 -
Excellent illustration
Thank You.
0 -
Since you have a 3 inch tapping on that boiler, I'd start with a maybe 3 x 12 inch nipple ( or as long as you can fit) and then reduce down to 2 1/2. That kills the velocity coming out of the boiler and its likely little or no water will ever make it to the header. This is a cheap way to really get the boiler performing well.
To learn more about this professional, click here to visit their ad in Find A Contractor.5 -
-
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements