Taco Vortech air separator
quickdraw
Member Posts: 2
in Gas Heating
I have a VTRTX125-3 Vortech air separator that is leaking water from the air vent. It has done this sporadically over the past couple of years then stops.It is not a lot of water just maybe 1/4 a cup.It seems to leak when system has not turned on in a couple of days.
I thought maybe the system was just adjusting.I have a Burnham boiler. Can this separator be opened and cleaned out if there is any dirt in it and how?
0
Comments
-
That vent is replaceable. IIRC it uses a 3/4" thread. It should unscrew in the normal manner.
No need to replace the entire Vortech.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
https://www.supplyhouse.com/Taco-418-4-1-2-FNPT-x-3-4-MNPT-Hy-Vent
Hy-Vent 418-4 (3/4" Male)
That is what is installed and can be replaced with.
Check the mesh vortex chamber to see if still intact. If deteriorated, the entire unit should be replaced as it won't be effective.0 -
-
-
Dave, that’s a great pictorial and great recommendation for removing vent.If they don’t remove top portion of casting, and attempt to unthread the vent, try fitting a dowel that’s same ID as vent in the vent before trying to torque it out using a pipe wrench.Daves way is best.Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions1 -
The replacement air vent on the -3 models ( VRTX125-3 ) would be 419-1. Older models, -1 & -2 would take 418-4. Hope this helps.
0 -
I would like to thank everyone who responded. The vent was on there really well. it took quite a bit of pressure to finally undo it. I couldn't undo mid piece as described in the repair picture because too many other pipes(some gas lines were in the way.But in the end it unscrewed and came off. So far so good. Thanks to all who responded
0 -
-
Quickdraw, what happened with the leak? Did it stop?
I have the same issue.
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements