Taco Vortech air separator

Options
quickdraw
quickdraw Member Posts: 2

I have a VTRTX125-3 Vortech air separator that is leaking water from the air vent. It has done this sporadically over the past couple of years then stops.It is not a lot of water just maybe 1/4 a cup.It seems to leak when system has not turned on in a couple of days.
I thought maybe the system was just adjusting.I have a Burnham boiler. Can this separator be opened and cleaned out if there is any dirt in it and how?

Comments

  • Steamhead
    Steamhead Member Posts: 16,861
    Options
    That vent is replaceable. IIRC it uses a 3/4" thread. It should unscrew in the normal manner.

    No need to replace the entire Vortech.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • dko
    dko Member Posts: 606
    edited April 18
    Options
    https://www.supplyhouse.com/Taco-418-4-1-2-FNPT-x-3-4-MNPT-Hy-Vent
    Hy-Vent 418-4 (3/4" Male)
    That is what is installed and can be replaced with.

    Check the mesh vortex chamber to see if still intact. If deteriorated, the entire unit should be replaced as it won't be effective.
  • SuperTech
    SuperTech Member Posts: 2,170
    Options
    Last time I ran into one of those there was no removing the air vent. My coworker tried everything he could to get it out and ended up destroying the air vent. I had to bring him a new air scoop and help him replace it. I'm pretty sure situations like that is why you don't see them anymore. 
    Mad Dog_2yellowdogAlan (California Radiant) Forbes
  • Dave H_2
    Dave H_2 Member Posts: 556
    Options
    Be mindful before you put a wrench on this and bangin away, here is the way to take apart
    Dave H
    kcopp
  • Joe Mattiello
    Joe Mattiello Member Posts: 707
    Options
    Dave, that’s a great pictorial and great recommendation for removing vent. 
    If they don’t remove top portion of casting, and attempt to unthread the vent, try fitting a dowel that’s same ID as vent in the vent before trying to torque it out using a pipe wrench. 
    Daves way is best. 
    Joe Mattiello
    N. E. Regional Manger, Commercial Products
    Taco Comfort Solutions
    SuperTech
  • SteveSan
    SteveSan Member Posts: 235
    Options

    The replacement air vent on the -3 models ( VRTX125-3 ) would be 419-1. Older models, -1 & -2 would take 418-4. Hope this helps.

  • quickdraw
    quickdraw Member Posts: 2
    Options

    I would like to thank everyone who responded. The vent was on there really well. it took quite a bit of pressure to finally undo it. I couldn't undo mid piece as described in the repair picture because too many other pipes(some gas lines were in the way.But in the end it unscrewed and came off. So far so good. Thanks to all who responded

  • psb75
    psb75 Member Posts: 838
    Options

    Very nice of the Taco guy to support his company's product. Information is invaluable. It maintains our faith in products.

    SteveSan