Taco Vortech air separator

quickdraw
quickdraw Member Posts: 2

I have a VTRTX125-3 Vortech air separator that is leaking water from the air vent. It has done this sporadically over the past couple of years then stops.It is not a lot of water just maybe 1/4 a cup.It seems to leak when system has not turned on in a couple of days.
I thought maybe the system was just adjusting.I have a Burnham boiler. Can this separator be opened and cleaned out if there is any dirt in it and how?

Comments

  • Steamhead
    Steamhead Member Posts: 17,385
    That vent is replaceable. IIRC it uses a 3/4" thread. It should unscrew in the normal manner.

    No need to replace the entire Vortech.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • dko
    dko Member Posts: 668
    edited April 18
    https://www.supplyhouse.com/Taco-418-4-1-2-FNPT-x-3-4-MNPT-Hy-Vent
    Hy-Vent 418-4 (3/4" Male)
    That is what is installed and can be replaced with.

    Check the mesh vortex chamber to see if still intact. If deteriorated, the entire unit should be replaced as it won't be effective.
  • SuperTech
    SuperTech Member Posts: 2,430
    Last time I ran into one of those there was no removing the air vent. My coworker tried everything he could to get it out and ended up destroying the air vent. I had to bring him a new air scoop and help him replace it. I'm pretty sure situations like that is why you don't see them anymore. 
    Mad Dog_2yellowdogAlan (California Radiant) ForbesEdTheHeaterMan
  • Dave H_2
    Dave H_2 Member Posts: 587
    Be mindful before you put a wrench on this and bangin away, here is the way to take apart

    Dave Holdorf

    Technical Training Manager - East

    Taco Comfort Solutions

    kcopp
  • Joe Mattiello
    Joe Mattiello Member Posts: 720
    Dave, that’s a great pictorial and great recommendation for removing vent. 
    If they don’t remove top portion of casting, and attempt to unthread the vent, try fitting a dowel that’s same ID as vent in the vent before trying to torque it out using a pipe wrench. 
    Daves way is best. 
    Joe Mattiello
    N. E. Regional Manger, Commercial Products
    Taco Comfort Solutions
    SuperTech
  • SteveSan
    SteveSan Member Posts: 261

    The replacement air vent on the -3 models ( VRTX125-3 ) would be 419-1. Older models, -1 & -2 would take 418-4. Hope this helps.

  • quickdraw
    quickdraw Member Posts: 2

    I would like to thank everyone who responded. The vent was on there really well. it took quite a bit of pressure to finally undo it. I couldn't undo mid piece as described in the repair picture because too many other pipes(some gas lines were in the way.But in the end it unscrewed and came off. So far so good. Thanks to all who responded

  • psb75
    psb75 Member Posts: 906

    Very nice of the Taco guy to support his company's product. Information is invaluable. It maintains our faith in products.

    SteveSan
  • gardenman
    gardenman Member Posts: 7

    Quickdraw, what happened with the leak? Did it stop?

    I have the same issue.

  • alanking
    alanking Member Posts: 1

    You don't need to take out the vent at all. Its core mechanism is replaceable. In most cases, you only need to replace an o-ring. I usually replace the o-ring 2~3 years. I got a bunch from ebay. They worked pretty well.

  • hot_rod
    hot_rod Member Posts: 23,396

    if fluid is running across the top from under the small cap, the issue is the needle valve inside is damaged

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream