Transformer with RWG Terminals. Sequence of Operation
  • HydroTech23
    HydroTech23 Member Posts: 2
    This is an original American Standard Transformer that supplies voltage to the gas valve. I need to replace it but its so old I cant find it.
    Steamhead Member Posts: 18,712
    What is the secondary voltage and VA?
    Consulting
    EdTheHeaterMan Member Posts: 12,507
    edited April 2024
    This is the replacement https://www.supplyhouse.com/Resideo-AT72D1683-Foot-Mounted-Plate-Mounted-or-Clamp-Mounted-120-Vac-Transformer-w-9-in-Lead-Wires-40VA
    A close look at the black cover shows 40VA
    Some assembly is required since this is a multi-mount universal transformer.
    edited April 2024
    Why did the transformer fail? Could be old age. OR there could be a failed section of wire insulation causing a dead short. If that is the case, you will be purchasing a second transformer if that short circuit is not corrected before connecting the new one.
    Try adding a fuse to the R terminal, then connect the red wire to the other side of the fuse. Like This
    I don't really sell these, Just get some fuses and wire connectors from the auto parts store.
    109A_5 Member Posts: 4,208
    Hello @HydroTech23,
    Looks like 24 VAC at 10 VA on the cover plate. So a transformer with the same secondary Voltage and the same VA rating or greater should work as long as there is no system defect that cause the original transformer to fail.
  • Sylvain
    Sylvain Member Posts: 155
    for a 24V transformer, chose the fuse (on the low voltage side) with a rating lower or equal to I=VA/24.
    EBEBRATT-Ed Member Posts: 20,482
    Looks to me like with R<W & G the old one is a fan center with maybe a relay on the other side that is not being used.