VS-3000 and 007e?
CC.Rob
Member Posts: 130
Wondering if a 007e ECM is a viable replacement for the original 007 internal circulator in a Burnham Revolution, which uses a VS-3000 to control the internal circulator speed. Thanks.
0
Comments
-
-
-
You are correct @kcopp From our PM:kcopp said:Similar to the Taco variable injection control.. Taco does not recommend an ECM pump to use in the bridge circulator position. You need the regular psc 007.
ECM circulators cannot be used with our PC controls. The PC controls modulates or chops the voltage signal to circulator, which is intended to limit the voltage thereby slowing the speed of the motor. That works fine with our standard PSC circulators like the 007-F5. However, the ECM product has an AC to DC converter in it, which turns it into a DC motor. The modulated signal from the PC705 will look like a low voltage scenario and the circulator with error on low input voltage. Regardless, this won’t change the speed of the circulator, it’ll just make act erratically and potential cause premature failure.1 -
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements