We have two Boilers heating house. One gauge shows 1 Psi the other 9 psi ?

Athana
Athana Member Posts: 105
edited March 18 in Strictly Steam
Hi. We have two boilers heating this house. JStar installed them 12 years ago (Joe) from here. I notice one boiler shows on the gauge 1 Psi but the other is 9 psi.
Should this be like this ?
Thanks

Comments

  • Steamhead
    Steamhead Member Posts: 17,387
    Pics? @JStar , you still here?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Athana
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,495
    One boiler probably has a bad gauge. The one reading 9 psi most likely.
    Mad Dog_2Athana
  • psb75
    psb75 Member Posts: 906
    Boiler gauges are on the system for a reason. If two gauges are on the same system they should read "the same" or within very close range of each other. Gauges DO fail i.e. get "stuck" or get plugged by debris.
    They are easy to replace and not expensive. Their main purpose is to show that your system is not "over or under" pressurized and that your system is properly "filled."
    Mad Dog_2Athana
  • neilc
    neilc Member Posts: 2,854
    or a pigtail is jelly
    known to beat dead horses
    Mad Dog_2Athana
  • Athana
    Athana Member Posts: 105
    Oh thank you so much : ) So no chance of it exploding or something.
    The Pigtails were cleaned at start of season to perfection (my wife got them from technician who was doing them in basement and took them to kitchen sink and cleaned them to perfection. : )
    JStar no more here..we loved that guy through and through.
  • Chris_L
    Chris_L Member Posts: 337
    edited March 18
    You say you have two boilers. Are they on completely separate systems? (For example if one boiler heats one part of the house, and the other another part.)

    If so, there is no reason their measurements should agree. And if both pigtails are clear, you need to find out why one is reading so high.
    BobCAthana
  • Athana
    Athana Member Posts: 105
    edited March 20
    New development. The one boiler gauge reading 1 psi I have kept running as it hasn't been cold..the one reading 9 psi I turned off. I expected if it is defective it would stay at 9 psi while off..but no, with boiler off it has dropped down to a little above 0.
    Both boilers heat the same area..Steam one pipe cast iron radiators..Smith Series 8 Boilers.
    Pigtails (Copper) were both cleaned before heating season in October...
    Gauges flawed ? Or other reason ?
  • reggi
    reggi Member Posts: 523
    @Athana ...I might of tried swapping the gauges .. .. just make the boiler isn't  steaming when you do this . . ..
    One way to get familiar something you know nothing about is to ask a really smart person a really stupid question
    Athana
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,519
    Pigtail is full of splunck...Mad Dog 🐕 
    Athana
  • neilc
    neilc Member Posts: 2,854
    why not post a picture of the Ptrol and pigtail, the sightglass, and LWCO,

    if you pull a wire from the Ptrol, can the boiler fire on a call for heat, it should not.
    known to beat dead horses
  • dabrakeman
    dabrakeman Member Posts: 645
    In your multitude of previous posts over the years since getting this dual Smith boiler arrangement installed you have repeatedly been asked for pictures so that the forum can properly help you out. You have also repeatedly been given local contacts in your area for expertise. Is there a reason you won't post pictures? If you do not know how then maybe we can help you with that.
    MikeAmannAthana
  • Athana
    Athana Member Posts: 105
    edited March 26
    Hi thanks Ive posted some pictures in the past but may have not known how in the earlier days. But for this one..the boiler was off and I wanted to be home when I turned this one back on to see gauge raise
    and I haven't been home for doctor visits. I ran the boilers for a few hours and these are the gauges.
    Picture #1 is at about 7 but was at 9 when I originally made this post..Ive had this boiler off since then.
    The other boilers gauge sits as you see around 2..maybe that one is the flawed one ?
    Im thinking to order two new gauges and have them replaced. When boiler was serviced Pigtails and these were taken off and well cleaned.I have attached other pictures of other gauges as well.
    Low Water Cut offs are two Cyclegards.
    Thank you


  • Athana
    Athana Member Posts: 105
    Other gauges.



  • mattmia2
    mattmia2 Member Posts: 10,955
    Are there zone valves in this system?
  • neilc
    neilc Member Posts: 2,854
    neilc said:

    why not post a picture of the Ptrol and pigtail, the sightglass, and LWCO

    I was thinking of more of an all in one shot so we see a more general view,

    well either the Ptrol is bad, or as well as the wife did cleaning the pigtail, something got missed at the boiler port, or under the trol,
    hard to choose one from this side of the keyboard
    known to beat dead horses
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,495
    like I said 14 posts ago your gauges are bad