Boiler feed pump overfilling

targetman74
Member Posts: 6
Looks like this has been going on for a couple years. Got called because of water on boiler room floor. The receiver is full, but the PRV is still feeding. Float problem?





0
Comments
-
Yes, it is on the RH end of the tank. There is a float inside like a toilet tank float. See what the water pressure is on the supply side of the float. I think 30 psi is max.
If the boiler pump is constantly cycling (like every 30 seconds) then you have a bad check valve between the boiler and the pump. If it doesn't get fixed you will kill the boiler.0 -
What is make up water supply pressure? Generally, mechanical float valves are not recommended when supply pressure exceeds 50 PSI.
What is regulated supply pressure downstream of PRV?
A better make up water arrangement is a float switch and solenoid valve.
Typically this is the preferred arrangement.Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.0 -
The PRV is 25-75 range. Someone wrote set to 20 PSI. First laid eyes on this yesterday. Thinking how could I add solenoid valve.0
-
@targetman
Take the original float out and install one with a switch. Wire the switch to the solenoid. Move the MU water to a different tapping. Put a tee in the vent line to add the water if you have to
Looks like a Shipco Tank? Call the local Shipco rep and they can hook you up0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements