Oil fired hot water heater continues to trip
Rodney10
Member Posts: 3
I replaced the Aquastat but it didn’t solve the problem. When I reset it fires and does not trip. After using hot water it trips periodically. What could be the problem? Possibly dirty nozzle?
0
Comments
-
-
You think the eye isn’t good. I watched a vid and will check it out0
-
The cad cell resistance doesn't tell you if the cell is good or not - it's a starting point to diagnose what's going on with the shutdown. An abnormally high reading could be a bad cell certainly or it's just as likely or more so to be a combustion issue.Rodney10 said:You think the eye isn’t good. I watched a vid and will check it out
0 -
Fuel supply ? How many units running off the oil tank ?
There was an error rendering this rich post.
0 -
We can all agree that an aquastat is not causing the problem.
If the burner is operating for more than 45 seconds then the primary control is probably fine. BUT There was an article about the old R8184G with the metal cover that was susceptible to a spike in electricity during operation that made the safety circuit partially engage the safety timer heating element. Then it would send a very small amount of electricity to that heating timer. Over time this would build up enough heat to trip the reset contacts. Those controls are so old that you probably don't have one of those, but if you have the removable metal cover R8184G primary control, you should replace it anyway.
If it is not the Primary control and it is not the aquastat, could it be the motor? Is there a dead spot on the motor that fails to start when the motor is warm, but it works fine when it is cooled down? I have had that experience before.
Could the fuel line or other part of the fuel system be compromised? After running for a longer time a clogged filter may slow the fuel down to the point that the flame goes out. We can fix that with a new fuel pump first and if it keeps happening then maybe check the fuel filter.
I have also replaced ignition transformers that worked fine when they were cold but failed to light the spark when they were hot from operation. If the burner cycles off by the limit, then within a few minutes tries to ignite again, that transformer would fail to make a spark.
How about the actual cad cell eye and the wiring harness that connects the eye to the primary control. That could be defective where heat can cause the wires or connections to expand and contract when the burner is warm from operation and when it cools down the poor connection is resolved.
After we spend lots of money on the primary control, a new motor, an ignition transformer, and several other expensive fixes, what should we check next? Those Cad Cell Eyes
are pretty inexpensive. Maybe you should try one of those, but wait until you change out some more expensive parts.
Too bad that there are no good oil burner technicians around anymore. You could sure use one right about now.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
-
The good ones are right here on the Wall!EdTheHeaterMan said:......Too bad that there are no good oil burner technicians around anymore. You could sure use one right about now.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I fixed it!!! Simple problem with a clogged up fuel pump filter. I replaced the filter and the nozzle. Yippee0
-
Rodney10 said:I fixed it!!! Simple problem with a clogged up fuel pump filter. I replaced the filter and the nozzle. Yippee0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements