Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Soot on aquastat
duh
Member Posts: 17
in Oil Heating
What could cause soot to appear on the inside of the closed cover of an aquastat mounted on top of a Buderus oil-fired boiler, model GS115WS4?
0
Comments
-
Convection currents would bring airborne carbon particles from incomplete combustion into the tiny openings of the control.OR
There could be an electrical restriction causing resistance in a wire. the insulation on the wire would overheat and start to burn and leave soot marks.
Look at the location of the soot and the wires around it.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Clean it and see if it returns.
The aquastat sits on top, near the rear of the boiler. Where is the draft regulator in relation?0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements