Heating device ID
mercedes
mercedes Member Posts: 67
Location NYC brownstone building. With heat emitters in the floor. This device with the blue knob on top with two tapping on the size . Need help to ID the device and functionality . thank you
  • bburd
    bburd Member Posts: 1,304
    edited February 2024
    That is an in-floor hot water convector, like a baseboard convector but set into the floor. The grille that should cover it is missing. They are usually installed in front of large expanses of glass, like sliding patio doors.
    The blue device is a balancing valve to regulate the water flow rate. The two small covered tappings on the side of this device are for differential pressure measurement, from which the flow can be calculated.
    Bburd
    mattmia2 Member Posts: 16,852
    aka a flowsetter or circuitsetter. The 2 ports have rubber plugs in them that special needles on the gauge set push through to measure the pressure on both sides to calculate the flow.
  • Big Ed_4
    Big Ed_4 Member Posts: 3,530
    What are they use for ? .... It almost looks like a scary burner :)
  • mercedes
    Yes I thought the same thing a scary gas valve. Gentlemen thank you.
  • ch4man
    ch4man Member Posts: 298
    save the shoe covers for clean floors... :)
    EdTheHeaterMan Member Posts: 12,225
    Circuit setters are used to balance the flow on a system that has several (many) branch circuits. A gauge woild be connected to the inlet and the outlet (the caps) of the valve and as the valve was turned, the pressure differential reading would indicate the flow thru the valve. This circuit setter would eliminate the trial and error method of balancing a system.
    I think the booties are more protection from what is on the subfloor.
    EdTheHeaterManold_diy_guyreggi