How often NTI combi boiler combustion chamber cleaning needed
harry_fine
Member Posts: 9
I have a new NTI combi boiler. It does heat and domestic hot water. Its at the one year old mark. Want to take care of it properly but don't want to spend money needlessly.
The opening up and cleaning of the combustion chamber and replacing igniter and gasket is an expensive job, i'm getting quotes for $650 Canadian.
Is this really something you need to do annually in addition to the DHW descaling which is another $350?
The opening up and cleaning of the combustion chamber and replacing igniter and gasket is an expensive job, i'm getting quotes for $650 Canadian.
Is this really something you need to do annually in addition to the DHW descaling which is another $350?
0
Comments
-
With natural gas , I would say 5 years , more so for the igniters and sensors . The condensate neutralizer , you can change yourself with a bag of marble chips .
There was an error rendering this rich post.
0 -
Thank you0
-
It depends on various factors..harry_fine said:I have a new NTI combi boiler. It does heat and domestic hot water. Its at the one year old mark. Want to take care of it properly but don't want to spend money needlessly.
The opening up and cleaning of the combustion chamber and replacing igniter and gasket is an expensive job, i'm getting quotes for $650 Canadian.
Is this really something you need to do annually in addition to the DHW descaling which is another $350?
1. Combustion air contaminants such as Pollen and Dust from dirt roads/nearby construction sites/Highways can contaminate the heat exchanger very quick!
2. Byproducts that are added to the Gas can contaminate the HX
3. A boiler that was not adjusted can contaminate the HX with Carbon.
A quick combustion test can reveal if the boiler is operating within specs.
Descalding frequency also depends on the domestic water quality...Well or city water?0 -
-
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements