Brazed plate HX on Greenstar
kcopp
Member Posts: 4,472
Has anyone had luck or should I say a way to flush out the boiler side of a BPHX on a Bosch greenstar boiler?
I have one that I'm 99% has gotten gummed up.
Boiler temp is running high in DHW mode and they are getting poor hot water.
I am hoping to be able to flush it out w/o removing it...
thanks.
I have one that I'm 99% has gotten gummed up.
Boiler temp is running high in DHW mode and they are getting poor hot water.
I am hoping to be able to flush it out w/o removing it...
thanks.
0
Comments
-
If you can isolate the boiler from the system, circulate a hydronic cleaner around the boiler and HX
what type of system, radiant, radiators, fin tube?
Has the system been taking on fresh water?
Unusual, but not impossible for the boiler side doesn’t get gunked upBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
The heat side of the system works fine. Its the dhw That is the issue. So when the 3 way valve switches the boiler water to the BPHX and it has restriction.
I have flushed out the boiler, installed a cleaner, Pulled every ferrous part out of the system and there was a magnetic filter added. Added inhibitor.
The fin tube is fed w/ 3/4" Poly butylene.
So it may take some working out of the junk in the system to get the water better.
How do I just get the BPHX boiler side flushed out instead of the boiler side? WITHOUT taking it out of the system...0 -
Without an extended dhw call, I guess the cleaner will not circulate through the HX,
if there was a way to force the 3 way valve to dhw you could circulate it?
Does it have a zone valve or solenoid?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Its a solenoid.
I was hoping someone had worked on this unit and could help me manually open the valve so I can flush out some of the junk. If you power it down it just stays in heating mode so flushing out that part is simple.
0 -
Have you cleaned and flushed the DHW side of the heat exchanger? that is usually the side that gets scaled up which will impede heat transfer and lead to lower DHW temps. If the boiler side of the brazed plate were getting gunked up I would imagine the boilers main heat exchanger would as well since it is significantly hotter there, and you would get issues on the heating side. Most of these flate plate heat exchangers in combi boilers are designed with the intent to completely remove them periodically for service. So long as this is similar you can completely remove the DHW heat exchanger and clean both sides of it.0
-
It’s not the domestic side w/ the issue. It’s the boiler side. When the 3 way valve switched to making hot water the pressure gauge drops and the boiler temp goes up.Yes I could remove… it wont be fun.The heat piping has a Caleffi dirt mag installed. I pulled both magnets and flushed this out today… odd enough it is not ferrous.0
-
Weird! Is it metallic like chunked up solder. Is it light weight like aluminum shavings?
Wonder if it is some drill shavings from the boiler or HX manufacturing process. Is that an aluminum block boiler?
I did see this same issue on a year old Viessmann combi. Once the contractor disassembled the HX from the block the boiler side was full of gunk like that.
The heat exchanger/ pump/ solenoid was a composite monoblock, the heat exchanger goes into the composite block with some O-ring seals. A bit of a task to get it out and apart.
The DirtMag will remove non ferrous particles like that. It is a multi pass device so some may have gotten into the HX before making it across the DirtMag.
The new XF "extra filtration" Dirt Mag was built with that in mind. The fine mesh grabs everything on the first pass. Designed to protect sensitive heat exchangers on A2WHPs.
https://video.search.yahoo.com/yhs/search?fr=yhs-ima-st_mig&ei=UTF-8&hsimp=yhs-st_mig&hspart=ima&p=caleffi+xf&type=q3000_A1BWP_set_bcrq#id=1&vid=d3a1cb863dabc4d33a534e8c35ef49db&action=clickBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
-
The greenstar is an aluminum block boiler. It looked more scale like.
I saved it and placed it off to the side.
Now I am wondering if the inhibitor I put in the system did one of two things... Reacted w/ the aluminum or is just scouring the 30 years of junk off the inside of the piping.
0 -
Boiler dope or sealer ?
There was an error rendering this rich post.
0 -
The previous boiler was a Trianco Heatmaker from what I understand.
It lasted about 20 yrs. I dont think they added any sealers. I did add cleaner to the system in October and it circulated for about 10 days before I flushed it out and added the inhibitor. oct 31st.
Most all the piping another contractor did 2 yrs ago.
Its 99% pro press.
0 -
Some #$% broke loose . 50+ old house ..
There was an error rendering this rich post.
0 -
So i did end up swapping out the FPHX. It was not the easiest and did require 2 sets of hands.
It was not the worst.
The only way to get the FPHX out was to drop the circulator and angle it out...
No room any other way.
I did have my silicone grease handy to have the parts go back properly.
Once that was in just a simple purge and the bleed out port.
I did add more inhibitor as I flushed out a good amount during the draining.
Im going to flush out the old FPHX w/ some vinegar.
Thanks all.
0 -
Did you cut open the old one with a PortaBand? Be interesting to see inside.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
The left manifold may be easier . Buying a new one comes with all the o rings , gaskets and hardware ...
There was an error rendering this rich post.
0 -
I didnt cut open anything. I was actually going to try to clean it out and have for that owner to have as a back up.
I did flush it out w/ water and got a similar colored scale solution .
0 -
I like the German engineering just not their instructions ....
There was an error rendering this rich post.
0 -
kcopp said:I didnt cut open anything. I was actually going to try to clean it out and have for that owner to have as a back up. I did flush it out w/ water and got a similar colored scale solution .Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements