Beckett Oil Furnace Hard Lockout Occurring every couple days
Kaitlyn
Member Posts: 8
in Oil Heating
My Beckett Oil Furnace keeps getting a hard lockout after the ignition trial fails. We cannot seem to diagnose the problem yet. Our mechanic has replaced the nozzle and the controller, but we are still getting a hard lock out. If anyone has any thoughts, please let us know.
0
Comments
-
Ideally, the technician should provide you with some information that would help diagnose the problem. Did he give you any combustion readings (something he would have done after replacing a nozzle), pump pressure, or ohms of the cad cell when running?Kaitlyn said:My Beckett Oil Furnace keeps getting a hard lockout after the ignition trial fails. We cannot seem to diagnose the problem yet. Our mechanic has replaced the nozzle and the controller, but we are still getting a hard lock out. If anyone has any thoughts, please let us know.
0 -
They replaced the nozzle, igniters were cleaned and cad cell replaced and the cad cell is now reading around 150-200 ohms once the flame is on.0
-
The running ohms is excellent. Is it going "poomph" when it's manually reset? (is it burning off excess oil after restart)Kaitlyn said:They replaced the nozzle, igniters were cleaned and cad cell replaced and the cad cell is now reading around 150-200 ohms once the flame is on.
If he's throwing parts at it, have him replace the ignition transformer and clean cut solenoid, and after that the aquastat I guess.
Did he bleed it after lockout and was there any air in the stream?
In any case, don't push the reset more than once at any one event.
1 -
Seems like an igniter but I'm not there.0
-
I would have him do an ohms test on the igniter and verify vacuum and pressure readings on the pump. If your tech is a certified technician have him call the Beckett tech service line. We work with tradespeople to help diagnose the service issue0
-
Yes it is burning off excess oil once it ignites finally. I poof of smoke comes out after the restart actually works. I will get him to check the igniter and hopefully that helps. If not I will let you know. Thanks for all the suggestions.0
-
Based on the burn-off, there is a high probability the ignitor/ignition transformer is bad. But first, the electrodes must be filed/shaped, and the gap and dimension adjustments around the nozzle must be within specification to guarantee ignition or a new ignitor won't help. If the electrodes are shaped and set properly, the ignitor is the next guess.Kaitlyn said:Yes it is burning off excess oil once it ignites finally. I poof of smoke comes out after the restart actually works. I will get him to check the igniter and hopefully that helps. If not I will let you know. Thanks for all the suggestions.
Remember, if the tech changed the nozzle, he must reset combustion - every nozzle is different despite the ratings printed on them.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 919 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements