Bock: new tank, new burner?
ferrociousghandi
Member Posts: 4
Most of my domestic hot water replacements are indirects, electric tank, gas combi boiler, or straight gas on demand. Never swapped a Bock oil fired 32E out. Can the old burner work in a new tank? I planned on a new burner with it but just asking if it is common to use the old burner.
0
Comments
-
What burner is currently being used?
3450 retention head?
Check the air tube and the head. Make sure nothing is warped or broken.
I would at the very least upgrade to a 15 second primary if not already.
If reusing the existing, get a new burner flange gasket.
You should have a combustion analyzer since you do the gas work. What you might not have, but will need for oil is a smoke tester. A pump pressure gauge wouldn't be a bad thing to have either.1 -
-