No air or water comes out of bleed valve at baseboard
RobAltman
Member Posts: 1
in Gas Heating
I went to bleed a baseboard radiator that was not getting hot, and I get nothing to come out. No water or air. My pressure gauge reads 20psi. All three zones are hot coming out of the boiler. Please help
0
Comments
-
Make sure the pressure gauge is not reading incorrectly. I often find them getting stuck and not going to zero when I drain a boiler. If you are not getting air or water out then either you have inadequate water pressure or a closed radiator valve.0