Air separators- pumping toward /pumping away

delcrossv
delcrossv Member Posts: 1,338
Going to put an B&G EAS+ Airtrol into a system. The present set up has the pump on the return (pumping toward).

Airtrol manual has this:



EAS manual doesn't specify




Although I know it's better to pump away, is it really worth repiping to have the pump downstream of the separator? Or is it "good enough" to leave the pump where it is. It's two loops , one pump with balancing valves.


Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.

Comments

  • hot_rod
    hot_rod Member Posts: 23,392
    What pump do you have? B&G 100 by chance?
    It is always best practice to pump away, but the juice may not be worth the squeeze.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • delcrossv
    delcrossv Member Posts: 1,338
    edited January 18
    hot_rod said:

    What pump do you have? B&G 100 by chance?
    It is always best practice to pump away, but the juice may not be worth the squeeze.

    Not that big. A B&G NRF-22. That's what I'm thinking.

    Apartment and in-law (basement) loops off a 4 section little Peerless.
    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • hot_rod
    hot_rod Member Posts: 23,392
    you would need to map or define the piping circuit to build an exact graph like this to see the ∆P.
    Or gauge it up.
    With 12- 15 psi I don't see a big problem.
    It's problematic air systems where the pumping away can be life changing.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • jesmed1
    jesmed1 Member Posts: 707
    @delcrossv Remember to use 3/4" minimum pipe to the Airtrol and pitch as steeply as you can. The 1" per 5 foot pitch they specify is a minimum.
    delcrossv
  • delcrossv
    delcrossv Member Posts: 1,338
    Should be going up at a 45 degree angle with this installation. Thanks!
    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    jesmed1