Air separators- pumping toward /pumping away
delcrossv
Member Posts: 1,338
Going to put an B&G EAS+ Airtrol into a system. The present set up has the pump on the return (pumping toward).
Airtrol manual has this:
EAS manual doesn't specify
Although I know it's better to pump away, is it really worth repiping to have the pump downstream of the separator? Or is it "good enough" to leave the pump where it is. It's two loops , one pump with balancing valves.
Airtrol manual has this:
EAS manual doesn't specify
Although I know it's better to pump away, is it really worth repiping to have the pump downstream of the separator? Or is it "good enough" to leave the pump where it is. It's two loops , one pump with balancing valves.
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
0
Comments
-
What pump do you have? B&G 100 by chance?
It is always best practice to pump away, but the juice may not be worth the squeeze.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Not that big. A B&G NRF-22. That's what I'm thinking.hot_rod said:What pump do you have? B&G 100 by chance?
It is always best practice to pump away, but the juice may not be worth the squeeze.
Apartment and in-law (basement) loops off a 4 section little Peerless.Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
you would need to map or define the piping circuit to build an exact graph like this to see the ∆P.
Or gauge it up.
With 12- 15 psi I don't see a big problem.
It's problematic air systems where the pumping away can be life changing.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
@delcrossv Remember to use 3/4" minimum pipe to the Airtrol and pitch as steeply as you can. The 1" per 5 foot pitch they specify is a minimum.1
-
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements